power= 1 x lead lamp 60w
1 x compressor (occasional use only) 2115 w (so 9A)
1 x heater (occasional use only) 1500w (so 6.38A)
power total = 15.38A (plus nominal lead lamp)
which is why i wanted a 20a spur, think i'm going back to get the guy to change the 13a spur box
Will you ever use the compressor and heater at the same time?? Also, the compressor only runs for what, 3 or 4 minutes at a time? The only thing i can see being in anyway restrictive is the starting current of the compressor, you may need to change the ring circuit B type MCB for a C type. Other than that i can't see a problem with your present loading...