power= 1 x lead lamp 60w
1 x compressor (occasional use only) 2115 w (so 9A)
1 x heater (occasional use only) 1500w (so 6.38A)

power total = 15.38A (plus nominal lead lamp)

which is why i wanted a 20a spur, think i'm going back to get the guy to change the 13a spur box


Will you ever use the compressor and heater at the same time?? Also, the compressor only runs for what, 3 or 4 minutes at a time? The only thing i can see being in anyway restrictive is the starting current of the compressor, you may need to change the ring circuit B type MCB for a C type. Other than that i can't see a problem with your present loading...
 
nothing sounds wrong really but not best practice having a 20a spur off a ring isnt the best option as your putting a heavy load on one point of the ring whuch isnt recommended
 
Your not a million miles off but in my opinion your leaving it to chance that your not going to be using to much current.

Good point from E54 about using a type C rcd and from Peter D.
 
thanks for the replies guys :) engineer54- i wouldn't have to run the compressor and heater at the same time but it would be preferable in order to dry spray paint.
Paulm- i see what you're saying actually. even just using kettle could take me over the 32a limit. iots a 3kw kettle so 13a on top of the 18a= 31a. getting near isnt it! i will only use the compressor and heater maybe once/twice a month but see what you're saying...........
 
I reckon the 13A supply from the FCU will be fine, not the best practice. Far better to run a 6mm T&E from the CU to connect to the 6mm SWA on a 25A/32A MCB then onto a 3 way garage CU. A bit more cash to dish out, but better all round...

The main point is, that compressors only run for a very short period to compress the air, then shut off until the pressure drops to a set level, before starting up again for another short period...
 
Last edited by a moderator:
I reckon the 13A supply from the FCU will be fine, not the best practice. Far better to run a 6mm T&E from the CU to connect to the 6mm SWA on a 25A/32A MCB then onto a 3 way garage CU. A bit more cash to dish out, but better all round...


i will look into this tomorrow in a bit more depth i think. my c.u is just inside the front door on the same wall as the front door at chest height and fully visible. will have to be careful with the plasterboard etc but will have a look tomorrow i think :)
 
ahhh yea thats what i thought, thankyou @)


just looking at the c.u. it is mounted in the hall at the very front of the house on full view to the right of the front door. it needs to get to the rear of the house. Thus it seems ( and i know you guys cant see my house! :) it's either a long ceiling run or underfloor run from the front of the house to the rear. not really wanting to have to pull up 1st floor or ground floor boards though.

Wish i could do it that way but just seems too much to do (especially with the nice oak flooring i have in the hall haha)
 
if, after a further invest tomorrow i cant run a new circuit from a spare way, and stick with the fused spur, do you think i should stick with the 13a spur or get a 20a one as i originally planned for, as obviously the 6mm swa cable can carry such a load out to the garage
 
Last edited by a moderator:
if, after a further invest tomorrow i cant run a new circuit from a spare way, and stick with the fused spur, do you think i should stick with the 13a spur or get a 20a one as i originally planned for, as obviously the 6mm swa cable can carry such a load out to the garage


Personally i'd first try it with the 13A supply as it's already in and see how it goes. If you have problems then start thinking about alternative arrangements. I think you'll find though, that diversity of connected loads is underestimated, an you'll probably be OK. Get yourself an amp clamp if you haven't got one, and check for yourself what sort of current your drawing in given situations. As i said though, you may need to change the MBC to a C type to take care of higher inrush currents from the compressor starts....
 
Can't really fault the practical advice above, just make sure you have some 13A fuses available! But really you should find you are OK.
On the wiring arrangement you could replace the garage socket with a small CU and have the SWA only fused by the ring OPD, but as stated above may have overload on the ring problems.
Done a quick possibility diagram of wiring for you.


Circuit layout.jpg
If your PIR does not have the fourth contact (L', or the like, usually for connecting another light) then you will not be able to switch it on permenantly
I would tend to put an isolator switch in for the PIR so you can switch it off easily for maintenance, but this is the basics.
You could change the R7 lamp in the PIR for a low energy one at about 24W to save power.
You may also find that the terminals of the lights are a bit tight for 2.5mm but so long as you do not need to double up you should be OK, you may need to change the terminal block in the flourescent for a 30A one to get the size.
Again if you can get any one in to do this would be a good idea.
 
Can't really fault the practical advice above, just make sure you have some 13A fuses available! But really you should find you are OK.
On the wiring arrangement you could replace the garage socket with a small CU and have the SWA only fused by the ring OPD, but as stated above may have overload on the ring problems.
Done a quick possibility diagram of wiring for you.

wow , thankyou for taking the time to draw a circuit. should help no end :). As you suspected, from memory when i wired the PIR the other day, it had four terminals but the fourth terminal had a black cable in it at both sides already. I dont know if it had L' on it though, i will check. But i got the 2.5mm in it without much hassle.
 
slight update, had a friend round today who's a domestic electrical engineer. He recommended similar as said on here; i.e taking the floor up upstairs, running 6mm t&E (down the wall into the 1 spare left in the c.u and along the upstairs underfloor to the rear of the house, eventually dropping down next to the socket i was planning on spurring off and out through the rear wall as i was going to straight into the 6mm swa.

Like you guys said, he thinks I may well get trips otherwise. One annoying thing upstairs is its wayrock floor so annoyingly have to cut holes in it :(
 

Reply to how to connect the following? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
124
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
493
Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
360

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top