Replacing Main Earthing Conductor | on ElectriciansForums

Discuss Replacing Main Earthing Conductor in the UK Electrical Forum area at ElectriciansForums.net

Clink

-
Joined
May 25, 2012
Messages
55
Reaction score
12
Location
Lincoln
This may be a newbies question but the older and wiser (or at least the more experienced) heads out there may be able to help....

Just inspected a clients house and amongst the, many, problems it only has a 6mm Main Earthing Conductor. I intend to upgrade it to 16mm but I can't see how to access the earth connector in the supplier's service head. Do I really need to contact the DNO to upgrade an earth? This seems excessive and possibly expensive.
 
The earth cable from the DNO head to the main earth terminal is the DNOs property and should not be changed by you.
You could ring the DNO and say that their earthing conductor is not suitable for the load but I would check this carefully with the adiabatic equation before you ring other wise you would be charged .
 
Thanks Richard, that's confirmed what I thought, I'll go back and check the sums but I'm pretty sure that they are correct. It does make it potentially an expensive bit of cable though.
 
Sorry Engineer54, but making the assumtion that it is TN-C-S just because the earth conductor enters the head is not really enough.
Many heads require that a link be connected inside the head to connect the neutral and earth.
It may be that this is a conversion that took place when 6mm² was the requirement, or may be that it is a TN-S system where 6mm² is still the correct CSA.
 
Sorry Engineer54, but making the assumtion that it is TN-C-S just because the earth conductor enters the head is not really enough.
Many heads require that a link be connected inside the head to connect the neutral and earth.
It may be that this is a conversion that took place when 6mm² was the requirement, or may be that it is a TN-S system where 6mm² is still the correct CSA.

You have far more experience than i Spin, on the types of Service heads and connection methods used by the DNO'S in the UK. Just that i have never seen a TN-S connection back home, that wasn't taken from the cable sheath below the service head. Even on a conversion, the sheath connection should be taken off/discontinued and the bare area insulated with amalgamating tape or similar...
 
Last edited by a moderator:
They used to use (and perhaps still do in some cases) a split concentric cable, where one half of the outer sheath was the neutral and the other half the earth.
These cables were often made off in the head, and unless the link between the neutral and earth was made, they were TN-S, but without removing the cover, there was no way to tell.
 
^^^^Yep, we have lots of this arrangement in my area. Check the PSCC and PEFC, if they are virtually identical, it's most likely TN-C-S (but with a 6mm earth, it's probably TN-S!)

Regards
 
They used to use (and perhaps still do in some cases) a split concentric cable, where one half of the outer sheath was the neutral and the other half the earth.
These cables were often made off in the head, and unless the link between the neutral and earth was made, they were TN-S, but without removing the cover, there was no way to tell.

Like this:

[ElectriciansForums.net] Replacing Main Earthing Conductor
 

Reply to Replacing Main Earthing Conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
418

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top