Have been advised by the Fire Officer that the supply to the stage area of our large club ( which supplies amplifiers etc for musicians) must be automatically isolated in the event of a fire alarm. At present they use a couple of 13A sockets which are on a ring main. I have no experience of this type of installation and will consult the people who service our fire alarm for advice what I would like would be some advice regarding placement of the contactor and also cable size for the radial which I imagine will be required to supply those two sockets, as I said this is a large club and the sockets in question are around 27 meters from the C/U, the fire alarm panel is only around 5 meters from C/U

Any advice gratefully received.
 
You are best to get a contactor to fit the distribution board
You may also need a manually operated emergency stop button wired into the contactor control circuit situated remote from the stage area,perhaps behind the Bar?
You would also need a switch on that control circuit to reset the sockets fed by the contactor
 
Might be better to bring the whole circuit out to a new small box (so take a feed from the main CU > cable to a new 4 way enclosure (Gewiss do one for about £10 with a clear lid would be perfect for this) > CPD ) and then just fit a 12V activated shunt trip to knock the circuit off. That way you can just take an aux straight off the alarm panel at 12v and it knocks the whole thing off, rather than having a contactor permanently latched. You have to manually reset them anyway. Hager do a nice one.
 
Standard request from fire officer, usually request house lights to be turn on aswell. For most small clubs, pubs we box up a contactor with reset switch. Contactors used have 24v coil, so straight into fire alarm, emergency buttons are twist rest type, diagram my help your spark.
[ElectriciansForums.net] Using a Contactor
 
Broadswood, they are wired in parallel using normally closed buttons, therefore when they go open the contactor is de energised

Thanks for that TAZZ, forgive my ignorance but as far as I can see BOTH of those emergency buttons would need to be operated in order to de energise the contactor...............no?
 

Reply to Using a Contactor in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Solved
Please use the like button to thank, like or whatever. As the forum treats that as a positive message then and uses it to score members.
    • Optimistic
Replies
11
Views
961
  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top