upgrading main earthing? | on ElectriciansForums

Discuss upgrading main earthing? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,278
Reaction score
5,773
Location
Gloucestershire
Evening all..

Just wanted a bit of advice about Earthing!! I'm not too sure whos responsibility the Earthing conductor is from the earth block to the cable sheath? It's 4mm and before I give out any certificate for a CU change I want to see 16mm. All other bonding and earthing needs upgrading as well but it was just this bit I was unsure about as I thought maybe its the DNO's field?


[ElectriciansForums.net] upgrading main earthing?

Cheers..
 
Thanks Telectrix.

Ze is 0.15. I will upgrade all my earthing and bonding bits to current regs but leave that bit. Am I still able to give a cert?
 
Yup. why not?

Just seems a bit odd.. I'll put down 16mm for earthing on the cert when I've upgraded my bit knowing that theres a 4mm link to the sheath from the earth bar.
 
Just seems a bit odd.. I'll put down 16mm for earthing on the cert when I've upgraded my bit knowing that theres a 4mm link to the sheath from the earth bar.

Quite agree with you but if the 4mm is fixed to the DNO head you can't change that and from your OP the Ze is fine so I'd be finishing off the cert and raising an invoice!
 
If that's an earth wire connected to a ring type clamp with a nut and bolt onto the lead sheath,I would and have changed these countless times,if not ignore me I have a mammoth job to see pictures anyway lol
 
If that's an earth wire connected to a ring type clamp with a nut and bolt onto the lead sheath,I would and have changed these countless times,if not ignore me I have a mammoth job to see pictures anyway lol

No nut and bolt, firmly soldered into place :smiley2:
 

Reply to upgrading main earthing? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
516
loz2754
L
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
They do a cy type with pur coating and it is even tougher but is shielded
Replies
3
Views
250
sounds like one of those jobs to swerve and let it be someone else's problem
Replies
12
Views
528
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks