AdieB

-
Joined
Apr 1, 2012
Messages
76
Reaction score
6
Location
Dorset
Testing at a house today. The supply is a TN-S. Earth taken from lead incomer cable. First test with my Megger 1730 gave me Ze of 3.5 Ohms, way above the 0.8 Ohms. Cleaned up the earth clamp and tightened it up and improved the reading to 1.7 Ohms. Tested from the live in the fuseboard to the lead sheath of the incoming supply with no earths attached and again achieved 1.7 Ohms. As this Ze value is the best that can be achieved what is my next action. Contact the local DNO and ask them to sort it, or Install an earth rod and change to TT system. This has obviously happened before top some body. Anyone help ------PLEASE.
AdieB
 
Just as a side project mate. Got to keep the wolf from the door :)
sometimes when i come home in a bad mood...i howl at the moon....

[ElectriciansForums.net] TN-S high Ze
 
Barry, I scent blood. Yours, very soon with the mood this lot seem to be in. A RCD is NOT the solution. At best it's a quick bodged fix.

I don't know Tony, There are a few here that seem to think an RCD is the ''cover-all'' answer to non performing TT systems!! When you think about it, it all boils down to exactly the same thing!! lol!!
 
If you selected a 3 wire configuration for measuring, then it uses a smaller current and is less likely to show-up a problem on a poor joint.

Use the 2 wire measurement as it's more likely to identify the problem!
 
Thing is I worry as depending on an RCD yet I think we have all had to return 1 or 2 faulty units


I think most here would shudder at the amount of RCDs (of all types) that were returned to manufacturer for replacement on my last and previous projects!! I'm expecting very little change on this project either. And, were talking of a top of the range manufacturer here too!! It's certainly opened my eyes on the reliability of RCD devices!! lol!!
 

Reply to TN-S high Ze in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K