Hello all..

I have recently added a spur for a customer and it got me thinking again about how many spurs could I actually take from the same socket!

The only socket I could use to take the spur from was on the ring and was already feeding a spur. Now I could have extended the ring but after a small amount of investigation I found that the existing spur was to a single socket hidden behind kitchen cupboards and never used so I disconnected and then fitted my spur.

It did make me think what was wrong with adding 2 spurs to the same socket though. The new socket was a crabtree and could easily accomadate 4 2.5mm conductors.

A double socket that is feeding a double socket spur has the (unlikely) potential to take 26A from the spur plus another 26A from whatever is plugged into it (therfore a maximum of 32A could flow through that one socket). By adding another spur to the socket the maximum it could take is not changed (still 32A).

I think the answer is that although possible its not a good idea to push the limit of a socket and by adding another spur I am pushing it closer to the limit of 32A more frequently which would be bad practice and unecessary as you can just extend the ring, but I'm thinking about it and need answers from the experienced chaps as otherwise I shall become frustrated!!!!
 
A double socket that is feeding a double socket spur has the (unlikely) potential to take 26A from the spur plus another 26A from whatever is plugged into it (therfore a maximum of 32A could flow through that one socket). By adding another spur to the socket the maximum it could take is not changed (still 32A).

!!!!
I might be misunderstanding this ?
 
I was quoting OP

Understood
[ElectriciansForums.net] 2 spurs coming from the same socket - NOT a spur from a spur!

I was only making available some information I had read
[ElectriciansForums.net] 2 spurs coming from the same socket - NOT a spur from a spur!
 
I changed a socket last week in a guys kitchen. It had three spurs off the ring in it! Five 2.5's do fit in a Crabtree socket, but by god did I swear! They all lunged out at me as I took the old socket off!
 
They might physically fit, but can you trust the terminal to make secure contact to all conductors at the same time? I can think of situations with four or five cables in one hole, three were clamped but the others fell out. Not an ideal setup, you must have put in some effort to get it back together as I can imagine the original workmanship not being of the best.
 
Hello all..

I have recently added a spur for a customer and it got me thinking again about how many spurs could I actually take from the same socket!

The only socket I could use to take the spur from was on the ring and was already feeding a spur. Now I could have extended the ring but after a small amount of investigation I found that the existing spur was to a single socket hidden behind kitchen cupboards and never used so I disconnected and then fitted my spur.

It did make me think what was wrong with adding 2 spurs to the same socket though. The new socket was a crabtree and could easily accomadate 4 2.5mm conductors.

A double socket that is feeding a double socket spur has the (unlikely) potential to take 26A from the spur plus another 26A from whatever is plugged into it (therfore a maximum of 32A could flow through that one socket). By adding another spur to the socket the maximum it could take is not changed (still 32A).

I think the answer is that although possible its not a good idea to push the limit of a socket and by adding another spur I am pushing it closer to the limit of 32A more frequently which would be bad practice and unecessary as you can just extend the ring, but I'm thinking about it and need answers from the experienced chaps as otherwise I shall become frustrated!!!!
when did 26+26 start equalling 32? it's 52
 
A 32A mcb doesn't act as a current limiting device! and btw, 52A would take about 10 minutes to trip a B type mcb and likely won't trip at all until about 47A being drawn, so the Regs say anyway.
don't underestimate the general publics' ability to abuse sockets. was called out to an office some time ago as they said their sockets were tripping to find a fan heater connected next to everyone's desk.they had 8 2kW heaters connected drawing 66A and the mcb still hung on for a few minutes after re-setting! in the last Regs you could spur off a spur but that's been changed obviously.
 
A 32A mcb doesn't act as a current limiting device! and btw, 52A would take about 10 minutes to trip a B type mcb and likely won't trip at all until about 47A being drawn, so the Regs say anyway.
don't underestimate the general publics' ability to abuse sockets. was called out to an office some time ago as they said their sockets were tripping to find a fan heater connected next to everyone's desk.they had 8 2kW heaters connected drawing 66A and the mcb still hung on for a few minutes after re-setting! in the last Regs you could spur off a spur but that's been changed obviously.

You could spur off a spur in the last regs ??? Daz
 
A 32A mcb doesn't act as a current limiting device! and btw, 52A would take about 10 minutes to trip a B type mcb and likely won't trip at all until about 47A being drawn, so the Regs say anyway.
don't underestimate the general publics' ability to abuse sockets. was called out to an office some time ago as they said their sockets were tripping to find a fan heater connected next to everyone's desk.they had 8 2kW heaters connected drawing 66A and the mcb still hung on for a few minutes after re-setting! in the last Regs you could spur off a spur but that's been changed obviously.

You could spur off a spur in the last regs ??? Daz

maybe the last regs book he possessed was the 13th?
 
Haha, maybe wirepuller.

That's a interesting question to be fair. Whats the oldest copy of the regs anyone holds? Or do you just bin them?

I've got a shyte load of books in the attic...im a hoarder when it comes to electrical information and publications.
 
As there is no MINIMUM distance that sockets can be spaced on a rfc.then in practice you could have 2 literally next to one another and have one spur from each of them. 3 or 4 inches of cable in between. Satisfies the regs but in practice is exactly the same as having 2 spurs from one socket, Thinking about it it is worse as there are now 8 outlets available...

[ElectriciansForums.net] 2 spurs coming from the same socket - NOT a spur from a spur!
 
Last edited:

Reply to 2 spurs coming from the same socket - NOT a spur from a spur! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
790
  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top