Hello all..

I have recently added a spur for a customer and it got me thinking again about how many spurs could I actually take from the same socket!

The only socket I could use to take the spur from was on the ring and was already feeding a spur. Now I could have extended the ring but after a small amount of investigation I found that the existing spur was to a single socket hidden behind kitchen cupboards and never used so I disconnected and then fitted my spur.

It did make me think what was wrong with adding 2 spurs to the same socket though. The new socket was a crabtree and could easily accomadate 4 2.5mm conductors.

A double socket that is feeding a double socket spur has the (unlikely) potential to take 26A from the spur plus another 26A from whatever is plugged into it (therfore a maximum of 32A could flow through that one socket). By adding another spur to the socket the maximum it could take is not changed (still 32A).

I think the answer is that although possible its not a good idea to push the limit of a socket and by adding another spur I am pushing it closer to the limit of 32A more frequently which would be bad practice and unecessary as you can just extend the ring, but I'm thinking about it and need answers from the experienced chaps as otherwise I shall become frustrated!!!!
 
That's true about the whole RFC they are only 2 legs unlimited skts within permitted square meterage and one sper permitted to each , if those skts are deemed to be likely to supply a heafty loading surley the installation design is at fault and not RFC witch 9/10 will serve occupants more than adequately
 
BS7671 433.1.103 and appendix 15 page 425 (you have got one of these, haven't you?).

very self explanatory. Unfused spur = 1 cable + 1 single gang or 1 two gang socket.
Doesn't say you can't have 2 spurs from the same point. Selection and erection criteria will apply though.
If extending the ring be very careful you don't create a figure of 8!
 
BS7671 433.1.103 and appendix 15 page 425 (you have got one of these, haven't you?).

very self explanatory. Unfused spur = 1 cable + 1 single gang or 1 two gang socket.
Doesn't say you can't have 2 spurs from the same point. Selection and erection criteria will apply though.
If extending the ring be very careful you don't create a figure of 8!

doesn't seem very good practice though even if it is technically allowed.i've only ever come across it in BIY (bodge it yourself!) situations
 
personally I think unfused spur in 2.5mm to a 2 gang is poor practice. Why not use 4mm?

funny you should mention that. i was thinking along the same lines. it's like a reverse lollipop circuit. in effect the 4mm would give you a 32A capability on the spur, so theoretically you could add more than 1 outlet on the spur.
 
[/QUOTE] in effect the 4mm would give you a 32A capability on the spur, so theoretically you could add more than 1 outlet on the spur.[/QUOTE]

Then you would be in departure from BS7671 and lots of onus on you to show equivalent safety. Agree this is possible though.

I work on 2x13 A load continuous, 4mm should be good provided installed correctly, i.e. no serious down ratting factors applied. Now totally safe and no chance of thermal overload. I do not like cable rated below breaker rating in ANY situation.
 
I work on 2x13 A load continuous, 4mm should be good provided installed correctly, i.e. no serious down ratting factors applied. Now totally safe and no chance of thermal overload. I do not like cable rated below breaker rating in ANY situation.

In theory it is limited by the fuses in the plugs that will go in the socket. In practice this sort of doesn't work because of unfused doublers etc.

A good example of where fusing down after a reduction in cable size does work is the old busbar chamber method. Tap off in smaller cables and switch fuse after the reduction. Just because the fuse is not immediately before cable reduction does not mean it's not protected.
 
Doing an EICR on a property and came to the kitchen, when i dropped the sockets my jaw also dropped, no end to end on the ring, one socket had the following spurred off of it - 3 double sockets, extractor hood, cooker ignition which then also had another socket spurred off that to feed a washing machine!!!! dropped another socket as looking for other leg of the ring to find a socket fed in 1.5mm!!! The guy has just had his kitchen fitted, looks all lovely and nice on the surface but really bad underneith. This was done by a Romanian builder who has no clue re electrics. I told the guy this needs to be sorted asap, i suggested he'll need a few fcus for the various spurs but it'll mean breaking a tile or two to put them in, cant really put any sockets below as cupboards already fitted, then try to find the other leg and put links between to make a complete ring, cant see any other way of doing it other then putting it on a 20A radial but that's not an ideal solution in my mind really, any other ideas? I thought you could only spur once off a socket unless you put an fcu then you can have as many as you like, didn't think you could spur out of a socket as many times as you can fit the cables into the terminal, doesn't sound like the right thing to do even if not in regs.
 
the 4mm on the spur can handle 32A, similar to 2 x 2.5mm if the rfc was extended. whereas a single 2.5mm is only good for 27A (clipped direct).
 
I was taught in college you could only take one spur off any point of the ring. Fine to fuse down to 13A then have as many sockets in a radial spur as you want, but only ONE spur per ring socket.

Now after being taught that I always took it as gospel that it was a reg, although i've never looked it up.
But having read the above posts i'm wandering if my tutor was right or not?
 
I was taught in college you could only take one spur off any point of the ring. Fine to fuse down to 13A then have as many sockets in a radial spur as you want, but only ONE spur per ring socket.

Now after being taught that I always took it as gospel that it was a reg, although i've never looked it up.
But having read the above posts i'm wandering if my tutor was right or not?

it's 1 outlet on an unfused spur off the ring, but if it's a fused spur, you can fit as many as you want.( within reason). see app. 15. bgb.
 

Reply to 2 spurs coming from the same socket - NOT a spur from a spur! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
792
  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top