M

munty12

Hello there. I'm forever looking over these forums looking for advice, and typically I always find an answer, except it seems in this one instance - which is what brings me on my merry way to here today.

I was thinking of running a new supply to the garage. Problem is it has a water pipe (only four inches of lead and the rest is poly!) so I need to earth it with a 10mm. The garage is only 1 metre away from the house. I dug a trench one metre long across the concrete path between the house and garage (about 300mm deep)

The length of the run is only 6M in total, so I thought I'd run a 10mm 3 core SWA, protected by a 1 way RCD CU, but someone else suggested running a smaller SWA supply cable with a seperate 10mm CPC for the water main - which makes obvious sense, right? This being the case, I wondered what are the recommendations for protecting a 10mm CPC in a domestic trench. From what I gather it has to provide mechanical protection and be anti-corrosive. Surely galv conduit is too extreme for this application? Is it okay to simply run the CPC in a PVC duct of some description? Is it ok to use polypipe?
Electrical Conduits | International

Which begs the quetion, if polypipe is considered to provide the correct protection, what's stopping me from doing away with SWA altogether and instead running the supply in twin and earth inside polypipe?

Much thanks for any suggestions.
 
I was thinking of running a new supply to the garage. Problem is it has a water pipe (only four inches of lead and the rest is poly!) so I need to earth it with a 10mm.

Potentially it may need bonding, not earthing. Have you performed any tests to determine whether this water pipe is an extraneous conductive part, if so what were your results?

The garage is only 1 metre away from the house. I dug a trench one metre long across the concrete path between the house and garage (about 300mm deep)

Are you planning to concrete back over when you're done? I assume so but if not then 300mm is not deep enough. Also, have you remembered your warning tape?

The length of the run is only 6M in total, so I thought I'd run a 10mm 3 core SWA, protected by a 1 way RCD CU, but someone else suggested running a smaller SWA supply cable with a seperate 10mm CPC for the water main - which makes obvious sense, right?

Erm, not really. If the water pipe is indeed an extraneous conductive part, I would be using the 10mm three core option, one of the three cores for a main bonding conductor (permanently crimped and extended within the garage board to the water pipe) and the armour for the earth.

so I thought I'd run a 10mm 3 core SWA, protected by a 1 way RCD CU

I would be installing the RCD within the new garage board rather than protecting it at the supply end. I'd take the feed directly from a spare way in the existing fusebox/DB via a steel adaptable box (or directly if you have a steel fusebox/DB), if no spare way then a small single switchable fuse housing would suffice. This is of course assuming that you're not on a TT system.

Which begs the quetion, if polypipe is considered to provide the correct protection, what's stopping me from doing away with SWA altogether and instead running the supply in twin and earth inside polypipe?

Forgetting the many regulations you would be breaching by doing so, common sense dictates that polypipe isn't that great at protecting cable from a spade. I would still duct the SWA though.

I'm guessing by your questions that you're not an electrician? I don't mean this in a patronising way at all, it's just that I'm in Brighton too so I'd be happy to send one of my guys over to give you a hand if you want to make sure a proper job gets done :)
 
Last edited:
Potentially it may need bonding, not earthing. Have you performed any tests to determine whether this water pipe is an extraneous conductive part, if so what were your results?



Are you planning to concrete back over when you're done? I assume so but if not then 300mm is not deep enough. Also, have you remembered your warning tape?



Erm, not really. If the water pipe is indeed an extraneous conductive part, I would be using the 10mm three core option, one of the three cores for a main bonding conductor (permanently crimped and extended within the garage board to the water pipe) and the armour for the earth.



I would be installing the RCD within the new garage board rather than protecting it at the supply end. I'd take the feed directly from a spare way in the existing fusebox/DB via a steel adaptable box (or directly if you have a steel fusebox/DB), if no spare way then a small single switchable fuse housing would suffice. This is of course assuming that you're not on a TT system.



Forgetting the many regulations you would be breaching by doing so, common sense dictates that polypipe isn't that great at protecting cable from a spade. I would still duct the SWA though.

I'm guessing by your questions that you're not an electrician? I don't mean this in a patronising way at all, it's just that I'm in Brighton too so I'd be happy to send one of my guys over to give you a hand if you want to make sure a proper job gets done :)
thank god someone finally had the sense to mention this...

as it was trundling along with no mention of the earthing arrangements...
 
Which begs the quetion, if polypipe is considered to provide the correct protection, what's stopping me from doing away with SWA altogether and instead running the supply in twin and earth inside polypipe?

Much thanks for any suggestions.

Isn't the question - is twin & earth designed/rated for burial ?
 
this'll sort out any shed.

[ElectriciansForums.net] Seperate CPC out to garage - duct or not to duct?you can just make out DS in the open hatch.
 
Maybe Rommel should offer his services to do it properly. I'm guessing that Munty12 is a DIYer...

My thoughts too, hence why I said I'd be more than happy to help. I fear that munty isn't going to take a blind bit of notice to the advice given though. He/she was on here reading the replies for about half an hour last night and never responded.

I hope I'm wrong though.
 
Hahahahaha!
Well, munty is more than welcome to engage my services to brush up on his tank operating skills :D

Is this a euphemism, or something! I'm scared now.
I'd be happy to send one of my guys over to give you a hand..


Now I'm terrified!

Thanks for all the sound advice guys. I was worried yesterday that the thread was going to slip down further and further into obscurity without so much as a peep from anyone, so I'm grateful for all the replies. I'd spent a while writing a full reply last night, and duly managed to delete it before I posted it. DUH!
I would be installing the RCD within the new garage board rather than protecting it at the supply end. I'd take the feed directly from a spare way in the existing fusebox/DB via a steel adaptable box (or directly if you have a steel fusebox/DB), if no spare way then a small single switchable fuse housing would suffice. This is of course assuming that you're not on a TT system.

It's a TN-S system. The house CU is plastic, with little space (it's crammed with RCBOs!)
Potentially it may need bonding, not earthing. Have you performed any tests to determine whether this water pipe is an extraneous conductive part, if so what were your results?

There is an old CU in the garage, and I found continuity between the tap and the light switch in the garage, when there is no sign whatsoever of a CPC between garage CU and said pipe (which is a little odd perhaps because there's 3m of plastic pipe between the point where the lead pipe comes in and where the tap is - I thought plastic was insulated, and that water was deemed a poor earth conductor).

So yes, the pipe is bringing a potential into the garage.

If there is only one pipe, what is the difference between bonding and earthing?
Are you planning to concrete back over when you're done? I assume so but if not then 300mm is not deep enough. Also, have you remembered your warning tape?

Yes I'm going to back fill it with a layer of sand, then solid concrete. Surely depth is decided by the need to protect it from accidental damage, such as a spade?
Forgetting the many regulations you would be breaching by doing so, common sense dictates that polypipe isn't that great at protecting cable from a spade. I would still duct the SWA though.

Someone could try to chop the cable with a spade, but they would only chip the top layer of concrete and make their whole body vibrate with the effort!

Or is it that the mechanical protection is also aimed at keeping the cable safe from a digger, or somesuch?
Erm, not really. If the water pipe is indeed an extraneous conductive part, I would be using the 10mm three core option, one of the three cores for a main bonding conductor (permanently crimped and extended within the garage board to the water pipe) and the armour for the earth.
Do I really need to thru-crimp the 10mm? Can't I simply terminate it at the garage CU, and then run a seperate 10mm CPC from the earth terminal to the pipe?
Isn't the question - is twin & earth designed/rated for burial ?

I guess that's the short-end of it. Just how good is this polypipe? If it is not considered strong enough to offer mechanical protection from a spade - what is it considered strong enough for? What's to stop someone running the stuff on the surface alongside a hedge to a shed or somesuch at the bottom of the garden? In theory, the shed could then be supplied by twin and earth.

Thanks again.
 

Reply to Seperate CPC out to garage - duct or not to duct? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
476
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top