Can anyone tell me if its possible to spur off a cooker circuit?

A cooker circuit is just a circuit .... apply the rules as you would elsewhere when taking a spur. Most cooker controlunits have a built in socket! But if its wired in 10mm you may not get it into the new socket ......
 
I have spurred of the cooker circuit before using 2.5mm^ (and 1.5mm before) to feed a FCU (fused at 3A) for the cooker hood, using the forward fusing rules 434 etc.., however you should not run other equipment other than that for the intended circuit, say a socket outlet off of the shower circuit should not be done (although I cannot find the actual reg that said this.)

In this case I did not add significantly to the load of the existing circuit, and it was for use alongside/with the said cooker.
 
Last edited:
The only part I can find is to do with ring finals, stating any loads above 2kW should be on their own dedicated circuit.

I was either taught that they should be seperate, or it was given as best practice advice at some point, or even maybe in one of the Nic books, then again it could even be an urban myth, either way I cannot find an actual reg actually forbidding it.
 
The only part I can find is to do with ring finals, stating any loads above 2kW should be on their own dedicated circuit..

Good old appendix 15? An 'informative' appendix as one way of achieveing reg 433. Good design is another way ..... Ive just never gotten around to being a good designer!

I cannot find an actual reg actually forbidding it.

You're not the only one, neither can I ......
 
Good old appendix 15? An 'informative' appendix as one way of achieveing reg 433. Good design is another way ..... Ive just never gotten around to being a good designer!



You're not the only one, neither can I ......

Yes and I looked through 16th ed AMD1 & 2, 17thed and the 17th AMD 1, think I will have a look at the 15th later, lol, like you say it probably has been taught as good design practice in the past, and just stuck.
 
Hi Guys,
the cooker circuit is done with 6mm cable and is protected by a 20ma breaker. i use the same size cable to the FSU from FSU i use 2.5mm cable to connect the extractor fan.

Just want to know if this is safe and comply with the regs
 
Yes he can, he could use 1.5mm from the cooker isolator to the FCU, so long as the length of his spur is less than 3m
 

Reply to Spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
The pics you put up of the consumer unit are all good .....all circuits RCBO protected and as above swap the fuse out for a 3 amp
Replies
2
Views
497
OK. Asking such a basic questions as this (and the answer is simple and I'll provide it in a second), my question to you is do you feel capable...
Replies
7
Views
883
https://www.lewden.com/products/socket-outlets-heavy-duty-ip66-ip67-ip68-ip69-metal-range/sockets-metal-range-ip66#product-related Up to 30A...
Replies
3
Views
297
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
217
  • Question
To avoid disappointment have no expectations. I wouldn't be surprised if that FCU was running warm with just 8A.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks