Lambretta phil

R c d tripping in main c/ unit in house think intermittent fault on cable to garage.disconected at both ends my steinel testers show fault between all conductors.my mates fluke and insulation testers show clear ,i test with mine again and fault . So when I go to get new cable I buy new fluke testers and with these ,yes you guessed it I get a fault. What am I missing.
 
Maybe your Steinal thingy and your digital tester were picking up some kind of induced or coupled voltage from another circuit in close proximity. If your mates insulation tester showed no fault and it was definately working then I'd take that result over the Steinal gizmo any day.


What was the original problem exactly. How frequently was the RCD tripping and was it only in wet weather for example. Do you have an earth leakage clamp meter in you tool kit?
steinel is just an AVI marvo...like this:

[ElectriciansForums.net] Fault or faulty testers

[ElectriciansForums.net] Fault or faulty testers

- - - Updated - - -

Hi glenspark what's Sils
scooters India LTD

- - - Updated - - -

indian Lammy....
 
Thanks Glenn, we're not big on those types of tester (or Indian Lambrettas for that matter) where I am. :)

If the SWA was a problem you'd almost certainly see a low insulation reading with a mega tester if you disconnected the armour at both ends and tested between the internal wires and the armour and between a known earth and the armour. This would indicate if the cable sheath had been damaged along the run somewhere. Replacing it without conclusive test results is a bit hit and miss.

The RCD is seeing the cumulative leakage of all the circuits it's supplying so an earth leakage clamp meter around the L+N of each circuit whilst they're live would be the best way of finding the leakage problem(s).
 
I used to use a steinel test lamp all the time,only trouble is they read a fairly high resistance on continuity,so holding wires onto the probes with fingers can give a reading,especially if fingers are moist.
 
Thanks specialist replaced cable as it was PVC t+e ,found joint under floor connectors in a box went in a tube under a path under stone steps etc so may not have been in tube entire route . Think been in about 20years so best to replace.
 
Thanks engineer54 I never said I didn't own a I R test kit my mate had his with him so we used his .we seem to have strayed from my main point of why 2 buzz testers show short and 1 buzz and 1 I R tester show clear.
 
.....why 2 buzz testers show short and 1 buzz and 1 I R tester show clear.
The reason you get different results from different testers is firstly because they're actually performing completely different tests. The IR tester is using a very high test voltage on a dead circuit whereas the volt testers are not using any test voltage on a live circuit.

Secondly the characteristics of the different voltage or continuity testers aren't the same. There will be a difference in their sensitivity and a difference in their input impedance so depending exactly what you're testing they'll often show different results.

Finally you need to use the right tester in the right way and test for the right thing.

Here's an example;
If an RCD is tripping occasionally and I suspect it's being cause by a cooker. Here's some tests I could do.

1. I could connect an earth leakage clamp meter around the cpc in the isolator and take a reading with the cooker on.
2. I could disconnect the cooker and use a continuity tester on the Mohm scale to test the resistance between the L+E and the N+E.
3. I could disconnect the cpc whilst the cooker is on and use a voltmeter with one probe on a known good earth to see if leakage is causing a voltage on the CPC.
4. I could use an earth leakage clamp meter around the L+N simultaneously at the isolator whilst the cooker is on.
5. I could disconnect the cooker and use a mega tester to test L to E and N to E.

All these tests will show some of the effects or the possible potential of the cooker to produce a leakage current to earth but only one of them will definitely give you an accurate indication of the actual earth leakage being detected by the RCD.

Like I said it's about using the right equipment in the right way and understanding exactly what the reading it's giving you means.
 
Thanks for that marvo think we will invest in a e l clamp meter.just to make it clear was using fluke /buzz testers on dead circuit as well . To see if conductors /earth etc were touching each other 2 said yes 1 said no with cable disconected at both ends.
 
I would say an earth leakage clamp meter is an absolute necessity for any electrician. There's a Dilog E/L clamp tester that has been given good reviews by a lot of guys on this forum and it's inexpensive by most accounts.

You can also get a discount from testmeter who are forum sponsors which might help.
 

Reply to Fault or faulty testers in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top