S

sparky6078

My boss has asked me to fit some MCB's that i feel doesn't offer enough discrimination, a 63amp c type mcb feeding a submains then out that submains is a 63amp b type feeding a circuit.

is this enough discrimination?
 
No
If in the below graph the B and C curves did not intersect at any point then full discrimination would be achieved, as the B and C graphs only separate over a short section there is a very limited discrimination.
[ElectriciansForums.net] Discrimination
 
That was my thought as well, would i be right in saying if it was a TT earthing system with 1 sec disconnection time it would be ok? (this is on a TN-S on the site)
Only if you could guarantee that your fault current would always be between 220A and 360A would there be discrimination between those two MCBs, other than that there is the chance that any one could go before the other.
 
With mcb's under short circuit fault there's little chance of having discrimination amongst any values of mcb to mcb .... from memory i believe a 6amp mcb gives full discrimination to a 63amp most other rating against each other will at most only achieve partial ...as fault currents can be in the 1000's and partial discrimination may only be up to a few hundred amps then its a free for all 'pot luck' to which will trip if not both together.

To provide short circuit discrimination usually requires larger cable install with upfront devices like 250amp mccb giving discrim' to 63amp down stream devices ... if your putting 2 mcb's in series regardless of rating this is usually poor design but the installation denotes the need to ensure discrim' as incoming services may be too small to achieve any full discrim' like a domestic.

So as you can guess its rare discrimination can be achieved in domestic and at most only partial so the 40amp mcb feeding the garage board with a 6 and 16 mcb's fitted will at most only achieve partial so a fault can still trip the upstream device but in a domestic environment this is not a big issue ... in a computer office it is.
 
My boss has asked me to fit some MCB's that i feel doesn't offer enough discrimination, a 63amp c type mcb feeding a submains then out that submains is a 63amp b type feeding a circuit.

is this enough discrimination?


Check your Ze and see your fault current, if it exceeds 1000amps then all mcb's 50amp and under will have zero discrimination between the types mcb with the same rating .. 63amp actually achieves a small partial discrimination if fault is over 630amps but less than 1260amps between a (C) and (D) ....as it is only partial either mcb is likely to trip with currents over 1260amps.

Any short over 630amps which is most installs will have no discrimination between your type (b) and (c) you are fitting

TBH if you are fitting too 63amp mcb in series i would say its poor design ... hope you have been slightly educated here and think its time your boss learns how to design a circuit to attain full discrimination.
 
Last edited by a moderator:

Reply to Discrimination in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I have changed the supply to a 16 amp mcb , my ZS at the bin store light is 1.29 ohms ,fault current of 186 amps. my read of the time current...
Replies
7
Views
808
  • Question
Reminds me of one where I got the DNO in to swap a L - N fused metalclad head in a church got talking to the 2 guys doing it the guy doing most of...
2
Replies
21
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top