I am only a trainee ( so don't bite too much) a friend of mine called out british gas to fix his boiler.. Whilst he was there he checked the electrics.. Said the earth loop was greater than 200 ohms on the ring main and they should get a spark out asap.. So he asked could i pop down and and have a look before they call in a spark ( to see if i could see what the issue was ) it is a TT supply as far as i can tell with a wylex board rewireable fuses with separate RCD installed.. Tested the board.. 0.28ohms..PFC was 0.956kA.. Tested the rcd at 1/2.. X1 and x5.. All within limits.. Tested the socket where the PLUMBER checked and here is where i get lost.. Earth fault loop impedance Test with a megger1730.. 1st test setting was L-L 0.60.. L-N was 0.60 and the setting l-pe was 800ohms.. Is the setting L-PE the important reading yes? And whats the outcome..
 
I have seen earth rods installed on TNS and TNCS systems. It can be confusing if you are not completly sure of what you are looking for. As has been said 0.28 is VERY low for a domestic TT system unless there a parallel paths e.g. shared metal water pipe with TNCS system bonded next door.
 
Confucius he say.......''don't listen to everyone at once, you'll git mixed up, go around in circles and disappear up your own backside''.
Sort out, for definite, whether it's tt, tns or tncs and then you might get somewhere with your question.
 
this is TT.

[ElectriciansForums.net] confused..
 
Confucius he say.......''don't listen to everyone at once, you'll git mixed up, go around in circles and disappear up your own backside''.
Sort out, for definite, whether it's tt, tns or tncs and then you might get somewhere with your question.
I don't know what he's on about but it certainly is not Chinese!!
 
Any idea why they would even be checking the electrics in the first place? After coming out to fix a leaky boiler.
Because the people who come out have sales targets to meet. They semi train them on elctrics and set them loose on an unsuspecting public, as a result little old ladies are coerced into replacing their 16th edition CUs for 17th ones because they've been CONDEMNED! because they're not safe.
Crooks.
I have that on good authority because I have a mate who is a pipe monkey who works for them.
 
Skelton.. They have recently had a new incoming supply fitted.. The reason i said tt system is because an earth is running outside to a rod.. My first thought was tns if that helps.. I should of took a picture would explain more as to why i got confused.. Im aware the fault is at the socket.. But is it as simple as finding a loose connection and tighten the earths up..
so...any evidence of a TN earthing then?
 

Reply to confused.. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top