Hi,

Customer wants me to fit him a 16A socket so that he can plug his caravan in, PME supply.

I wouldn't call his drive way a caravan site, so not exactly sure if I should be doing this as it could be potentially dangerous as I was just planning on hooking up the earth as well, but then thought would it need a rod?
 
I would not connect the PME system earth to the outdoor socket, I would put that one socket on it's own 30mA RCD and on it's own rod.

The RCD would be incorporated with that socket, and the rod local to it. (fed from a non-rcd way at the house)

It is not so much that the garden is not a caravan park, but more the difference between 'true earth' and the PME earth, bear in mind the caravan body and chassis is bonded to the earth locally at the van side.
 
Just thinking about this, it does clearly state in the regs that you don't take the earth to a caravan, which I knew.

I think I'll just tell him to stick with him after lead and plug it in to his 13a plug.

All I was going to do is change a faceplate for a commando socket basically for ease.

Whats the difference in having a proper socket or using an adaptor, the 13a plug version has the earth connected still, just I didn't do it.
 
As I said if you earth the van with the PME earth, you would have a bloody big piece of metal (the van) that may be at a different potential to the true earth (the garden), then the usual broken suppliers Neutral scenario also rears it's ugly head, the car charging points regs are the same/similar for the same reasons.
 
Just RCD/TT that socket.

It is for safety reasons, just think if the Van body became live because of a fault, and you were stepping in or out., one leg on the garden and one leg in the van, it basically covers your arse in the unlikely event blah..blah
 
As I said if you earth the van with the PME earth, you would have a bloody big piece of metal (the van) that may be at a different potential to the true earth (the garden), then the usual broken suppliers Neutral scenario also rears it's ugly head, the car charging points regs are the same/similar for the same reasons.


Except you can now use a PME supply for a car charging point!!

If this is just for a caravan battery charging point isolate the house earth and use a roded earth. I wouldn't be going overboard on the Ra values either, unless they intend to use that supply for anything other than charging the battery....
 
Except you can now use a PME supply for a car charging point!!

It is not quite as cut and dried as that E54, there are a number of caveats attached to your statement above.

It is too much of a generalising statement to say you can use PME for car chargers, yes you can but only if other circumstances/conditions are met, ie. it is conditional. or you have a very good reason for the exemption clause.
 

Attachments

  • 17th Amd 2 part.pdf
    131.2 KB · Views: 68
Last edited:
It is not quite as cut and dried as that E54, there are a number of caveats attached to your statement above.

It is too much of a generalising statement to say you can use PME for car chargers, yes you can but only if other circumstances/conditions are met, ie. it is conditional. or you have a very good reason for the exemption clause.

Point taken, i was aware, but to rattle off all those conditions/provisions and it would have been a hell of a long post. lol!!.

It's a shame the DNO's don't insist on the provision of an earth rod for all PME/TNC-S installations, as they do in most other Western European countries....
 
As I understand it you can if you disconnect the PME earth.

The funny thing is, you could just get an adapter from a 16A to 13A plug top and plug it in on a PME anyway with no earth rod....

Do you feel that such adapters should be banned then.
 
UKsparks,

What you do is entirely up to you, we can only advise where you stand wrt regs, and why it is not a good idea to use the PME system earth for a caravan, whether it is in a park or the garden.

TT an TN-S supplies are no problem, it is only TNC-S/PME which gives problems on this type of install

Yes, you segregate the earths. here are the various drawings, although these are for full caravan pitches, the same principle applies to a single socket, Drawing 02 is the nearest one for your single socket, I have just included the others for information.
 

Attachments

  • [ElectriciansForums.net] Caravan charging point / 16A Socket
    caravan 01.jpg
    56.4 KB · Views: 41
  • [ElectriciansForums.net] Caravan charging point / 16A Socket
    caravan 02 001.jpg
    67.9 KB · Views: 44
  • [ElectriciansForums.net] Caravan charging point / 16A Socket
    caravan 03 001.jpg
    74.5 KB · Views: 31
  • caravan 01.pdf
    65 KB · Views: 28
  • caravan 02.pdf
    76.5 KB · Views: 24
  • caravan 03.pdf
    83.2 KB · Views: 26

Reply to Caravan charging point / 16A Socket in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
730

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top