Hi, new here. Just a quick question regarding a recycling plant panel I've been tasked with fixing.

Basically there are a few relays that pull in once the panel is made live, but 2 of 5 of these relays are "chattering" and not fully holding in. They have 120v coils and the input voltage is currently 60-65v. I understand the main apparent issue, but my question is why don't the other relays have the same issue if they're all getting the same voltage? Also would the "chattering" issue be fixed by replacing the panel transformer for new?

Any help or advice would be greatly appreciated!
 
If a relay or contactor is getting a high enough voltage to pull it in then that same voltage is more than sufficient to hold it. Retest the output of the Tx using an analogue tester and only test secondary voltages across both sides of the secondary ie don't test wrt earth or neutral.
 
Faulty transformers don't usually give out wrong voltages. If any part of a winding goes open-circuit you get nothing, and if it shorts the transformer burns out or blows its primary fuse. I reckon it's more likely that there is a wiring fault putting something in series with the coils that are showing suspect volts. I notice that 60 is half of 120 - have the two coils ended up in series with each other? As per Marvo test across the TX secondary terminals directly. If incorrect, check that the correct primary tap has been used for the supply.
 
Although it shouldn’t be, is the control supply centre tapped? Was just about to agree with Lucian but thinking about it if the return is lost then both relays will have an equal supply.

Sorry, there’s too many variables to give an answer. Get testing kid!
 
Your coil supply could be high impedance, your testers sampling rate could stop you seeing the voltage rise and fall and giving you an average voltage relating to peak and duration... -

Drop the wires off the coil and measure again it could be a faulty coil dragging the power down.
Check for short circuits of the TX within the controls most likely on any control wires to a N/O output of the chattering relay.
Do you have a wiring plan and can you post it .
What is your experience with control systems? and what is your electrical background.
Is this a new set-up you have just powered up or an existing one that's been working fine until this happened.

As mentioned already Id be surprised if faulty TX, if your connecting all this up and you have yet to get it running then highly likely you have a wiring error, if existing that has gone faulty then you need to understand how the TX secondary side is set-up to be able to test as coil feedback will make you think voltages are present and ok in parts of the circuit when they are only feedback... is your TX grounded on the secondary in any way to give you a reference?
 
Do you have a wiring plan

AAahhhh we all have dreams....


Its great feeling when you open up the panel and find the drawings inside...

[ElectriciansForums.net] Panel relay/transformer issue


But more often its ....


[ElectriciansForums.net] Panel relay/transformer issue



ha ha
 
True... was faulting a machine the other day and opened panel an NO WIRING PLANS!!!.. so the longer method to resolve the issue. Customer hovering over me said he hasn't any plans either then said all the cables are numbered won't that tell you what they are?..I said its like finding a street in a strange town without sat-nav or a map and all the street names have been replaced with numbers... all you can really benefit from it is you can easily figure if you find the other end of the street as it still has the same number on it... he went Oh! :charming:
 
...Similar scenario for me last week working on a settling plant control board,no drawings,but operator had drawings for a similar,older plant..."any use?" he says,Yep i replied,in the same way a 1970's A to Z would help you get about today...a pointer,but you still end up askin' a stranger for help...
 
The plant operator can be your best friend or your worse enemy. He knows how the plant works and so can help with the sequence. The problems start when he wants to sit on his arse, then you’re up the creak without a paddle.

Older plants drawing are a luxury, if you can find them you will have to piece them together first. Then comes translating the scrawled modifications done over the years.
 
I would lie awake at night dreaming of a scrawled scribble of any modifications...Luxury...sometimes the best they can offer is a mobile phone number of a lad who used to work with the electrician who left...but now has a mobile pig spit roast business...(actually true!) :cry_smile:
 

Reply to Panel relay/transformer issue in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top