NigelMarsh

I have been asked to get the emergency lighting working at a nursery. They had a switch put in at the entrance to the building that switches off all of the lights in the building when they lock up at the end of the day. All lighting circuits are hanging off a contactor connected to this switch, so they are cutting power to the light circuit MCBs and pretty much simulating failed circuits when using this, "master" switch.

whoever fitted this switch saw this and wired all of their emergency lighting into its own circuit to prevent it kicking in when the lights are switched off in the evening.

this obviously makes the emergency lighting pretty much useless for its main function.

they don't want to get rid of the master switch, but the want the emergency lighting to kick in when it's local lighting circuit fails. Doh!

Any ideas on how this can be achieved without losing the master switch, even if it means switching all lighting off using a different method? I'm going grey trying to come up with a simple solution.

:banghead:
 
I have been asked to get the emergency lighting working at a nursery. They had a switch put in at the entrance to the building that switches off all of the lights in the building when they lock up at the end of the day. All lighting circuits are hanging off a contactor connected to this switch, so they are cutting power to the light circuit MCBs and pretty much simulating failed circuits when using this, "master" switch.

whoever fitted this switch saw this and wired all of their emergency lighting into its own circuit to prevent it kicking in when the lights are switched off in the evening.

this obviously makes the emergency lighting pretty much useless for its main function.

they don't want to get rid of the master switch, but the want the emergency lighting to kick in when it's local lighting circuit fails. Doh!

Any ideas on how this can be achieved without losing the master switch, even if it means switching all lighting off using a different method? I'm going grey trying to come up with a simple solution.

:banghead:
Feed the emergency lights from the feed side of the contactor from the MCB, you can even add the test switch for them at that point.
 
I cant see 3 phases feeding individual lighting circuits via the contactor, so if one phase was lost then em lights on that circuit would illuminate, and normal lighting would go out.....unlike control, its not dependent one all 3 phases
 
The reason I bought this up tazz is I’ve had two phases fail feeding a lighting contactor. ⅔[SUP]rds[/SUP] of the place blacked out and no EM lighting. To be honest I pulled the fuses to prove a point.
I don’t know who designed the set up but I know there was an arse kicking party afterwards. I don’t even know why I got involved, lighting and small power wasn’t my job.
 
Can see where you coming from..but here any phase that fails, will bring on the Em internal battery on that circuit, so even if all phases go out, it should course a problem...if it was a sustained central battery system, then this would need fail safe features
 
Hi,
You have missunderstood, the em lights if they are the maintained type have a perm live feed and and a switched live feed. If the supply to daily switching contactor fails then the switched live drops out but the perm live from the local supply is still live, so the light is not lit even if there is a fault to the contactor. If you have a second contactor in the perm live, with the COIL fed from the same COIL supply as the day switching contactor then a fault will then cause the perm live to be disconnected and the EM run from it's battery.
 
Hear what you say...but the lights switching off with their charging lights still on, would be an indication of fault on daily switch feed, fault on perm feed would result in em coming on off their own battery.
Hope old diagram will show
[ElectriciansForums.net] Emergency lighting on contractor switched lighting circuits
 
Can see where you coming from..but here any phase that fails, will bring on the Em internal battery on that circuit, so even if all phases go out, it should course a problem...if it was a sustained central battery system, then this would need fail safe features

As I said, I had little to do with them but I think you’ve hit the nail on the head. There was a central battery room in each of the intake subs which fed out to the various plant subs.
I gave them a wide berth, the mates looked after lighting and batteries. The only time an electrician got involved was if one of the central lighting panels failed.
 

Reply to Emergency lighting on contractor switched lighting circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
1K
davesparks
D
Neutral and live
Replies
2
Views
317

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top