hoppy

-
Joined
Mar 8, 2009
Messages
163
Reaction score
18
Location
Liverpool
Hi I was testing a ring circuit and got some weird r1 r2 readings and just wondered if any one could shed a bit of light as to why as I am a bit puzzled. It is a periodic test!

13 sockets on ring one of which is spur, 2.5 / 1.0 twin and earth!
end to ends done at socket as board a bit messy!
r1 = 0.65
Rn = 0.65
r2 = 1.58

end to ends are ok.
Was expecting. 0.56 r1r2.

but the r1r2 readings I was getting were quote varied, one socket I got 0.50 and some others 0.53, others 0.55 and others 0.57 and that is to the terminals with the socket off the wall!

Yes I had the correct legs linked out!
could this be a ring within a ring! Also do you think this should be a code as all results are acceptable but just seem to vary a bit more than expected!

the socket I got 0.5 at is defo part of the ring!
what do u think!

oh possibility of joints under floor were kitchen sockets have been taken from
general ring, and put on their own circuit.
 
As above,unless it's a 2' square wendy house,sleep well :stooge_curly: ...and if you want to get those end to end readings perfect,shorten the cpc a bit...
 
Last edited:
Thanks guys for the replies, just seemed a little odd, most rings I test are pretty spot on, I.e within a couple of ohms, just my inexperience I suppose, thanks for putting me at ease!
 
Hi I was testing a ring circuit and got some weird r1 r2 readings and just wondered if any one could shed a bit of light as to why as I am a bit puzzled. It is a periodic test!

13 sockets on ring one of which is spur, 2.5 / 1.0 twin and earth!
end to ends done at socket as board a bit messy!
r1 = 0.65
Rn = 0.65
r2 = 1.58

end to ends are ok.
Was expecting. 0.56 r1r2.

but the r1r2 readings I was getting were quote varied, one socket I got 0.50 and some others 0.53, others 0.55 and others 0.57 and that is to the terminals with the socket off the wall!

Yes I had the correct legs linked out!
could this be a ring within a ring! Also do you think this should be a code as all results are acceptable but just seem to vary a bit more than expected!

the socket I got 0.5 at is defo part of the ring!
what do u think!

oh possibility of joints under floor were kitchen sockets have been taken from
general ring, and put on their own circuit.

Getting your rrRR's mixed up.........could get hung, drawn and Quartered for that.
 
For an RFC in older 2.5mm2 cable, where the CPC is only 1.0mm2 (instead of 1.5mm2), which is what you appear to have, the variation in (R1+R2) is greater (than if standard 2.5/1.5 cable).

My own house is like this, and I calculated (from r1, rN, r2) a few years back (in Excel) that the (R1+R2) could vary from as little as 0.603 (for a socket more or less at the origin) to as much as 0.733 Ohm (socket mid-RFC). In practice, the results at the time varied from 0.64 Ohm to 0.75 Ohm, discounting a few spurs.

I just put your r1, rN, r2 values into the Excel sheet, it gave results from 0.46 Ohm at origin, 0.49 Ohm at 10% from the origin, to max 0.56 Ohm at mid-point.

The simplistic +/- 0.05 Ohm doesn't take into account these older circuits, where CPC is much smaller than L/N conductors.
 
Last edited:
Here's a pretty graph showing you the variations in (r1+r2)/4 for different ratios of line conductor and CPC. 2.5+1.0mm is the dashed red and cyan line (being identical to 10+4mm).

[ElectriciansForums.net] Weird readings!
 
Thats interesting Steve. I have to admit I thought R1+R2 pretty much always = (r1+r2)/4. This diagram shows that one could be up to 20% lower than the other!
 
When you measure the figure of eight testing then you are effectively measuring the worst case scenario at every point in the circuit because of the interconnections; the fact that each measurement should be the same (allowing for variations in contact resistance), due to the cable connections you have made, allows you to assess if there is anything wrong at any point in the circuit.

However in practice the actual R1+R2 you would get at sockets at varying distances from the CU is as in the graph above, the R1+R2 = (r1+r2)/4 is only found at the mid point of the circuit.
For testing purposes this is the highest value (apart from spurs) that you will get and so the circuit must comply with that value as the worst case.
This is the same as when measuring a radial circuit where your R1+R2 increases with distance away from the CU and the highest value is the one recorded.
 

Reply to Weird readings! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
Recommend this: Electricians Guide to Inspection and Testing Book -...
2
Replies
18
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top