Put it this way; if you had used a Megger 15xx, the ring circuit readings would have off the scale as it only goes up to 299M at 500v.
I've spent all day getting a circuit from 0.00M to 5M before now and gone home pretty happy!
Well when you put it like that :D

Thank you mate!
 
Put it this way; if you had used a Megger 15xx, the ring circuit readings would have off the scale as it only goes up to 299M at 500v.
I've spent all day getting a circuit from 0.00M to 5M before now and gone home pretty happy!
Agree, the Dilog tester I have only goes up to 200M these readings are fine!
 
If you are seeing several 10Ms or more, and especially if it increases as you keep the test voltage on it, then I would not worry.

Edit: Look up "Polarisation Index" or "Dielectric Absorption Ratio" if you want some more info.
 
Last edited:
I was at the other end of the results spectrum today.
As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf and not the simplest to work for. She lives alone in a large detached town house. Consumer unit is in "the cats room", I gave serious thought to bringing some 20mm conduit in to breathe through.
Anyway, right hand RCD wouldn't stay on. Quickly traced to socket circuit, 0.00M.
After shouting various questions and getting nothing very useful back I worked out which sockets were served, unplugged things one at a time, and unplugging an extension lead caused a leap to 27M. That will do for 6pm when she's made it very clear she's waiting to watch Wimbledon.
"Oh yes I was mowing the lawn when it happened". (nice of you to mention it afterwards)
 

Reply to What causes low IR readings? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
664
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top