    megger 1720

    Hi, I have a mft 1720, the equipment itself is brilliant but every so often when I test earth loop impedance the rcd trips before it gets a zs value. On the same system I tried a older mft and got a zs reading straight away. Any suggestions
  2. W

    mcb keeps blowing on lighting

    I looked at the schneider rcbo earlier and manufacturers guide in a bold statement says not to be used on tt or tns ,I looked at wylex proteus lewdon and m2 and none of them state they can't used on a tt wholesellers I go in did not have 1 sp+n rcbos
  3. W

    mcb keeps blowing on lighting

    So the sp rcbo would operate on a n & e fault being pme . I ave just ordered some dprcbos expensive lesson this is but needs to be done . Thanks for your help mostly appreciated
  4. W

    mcb keeps blowing on lighting

    Thanks for that davesparks that makes perfect sense . If the earthing was pme would the sp rcbo be ok to use
  5. W

    mcb keeps blowing on lighting

    Will have to take rcbos out and install a 17th d/b and just take it as a lesson learned
  6. W

    mcb keeps blowing on lighting

    So why are they total crap. I will just admit my mistake what every one seems to no everything about and change the rcbos for dp rcbos .I don't think I'm a no it all one bit just because I thought I was right in what I was saying but I was wrong admittedly I can see how that makes me a no it all .
  7. W

    mcb keeps blowing on lighting

    You didn't explain about the sp rcbos on a tt system
  8. W

    mcb keeps blowing on lighting

    Is that a regulation in bs 7671 that sp rcbos are not recommended on a tt system if so what page number is it
  9. W

    mcb keeps blowing on lighting

    Explain then, I fitted proteus sp rcbo 30mA, I always thought that rcbos are the best protection to have in domestic due to it being less disruptive to other circuits if a fault occured. I'm sure your gonna have a lot to say about this
  10. W

    mcb keeps blowing on lighting

    So a 16 th edition c/u is perfectly safe then on a tt earth arrangement ??? What about the earth fault loop impedance being to high to provide the correct disconnection on the circuits not protected by a 30mA rcd ??
  11. W

    mcb keeps blowing on lighting

    I explained to the customer about the difference between rcbos and 17th edition d/b and the customer agreed on the rcbos.on the old d/b all the lighting was not protected a shed supply and cooker supply also was not protected by 30mA rcd .Any cables buried less 50mm has to be protectected by a...
  12. W

    mcb keeps blowing on lighting

    Thanks for most of the replys it ended up being a squished cable in the loft from a walk board on to and the c/u was not up to date to the 17 th edition 7671 so replaced with rcbos.tested dead and live test all performed and passed and certified and logged on to building control .so there...
  13. W

    mcb keeps blowing on lighting

    Hello sparks I was at a Job earlier today,the customers upstairs lights would not turn on due to the 6A mcb operating so it's a short circuit so I disconnected the supply to the first light the supply disconnected from consumer unit ,then did a insulation resistance which came out clear tried...