Hello sparks
I was at a Job earlier today,the customers upstairs lights would not turn on due to the 6A mcb operating so it's a short circuit so I disconnected the supply to the first light the supply disconnected from consumer unit ,then did a insulation resistance which came out clear tried the mcb without any connection it stayed on.so connected the supply at consumer unit and left the other end not connected to anything it stayed on so connected the loop out and switch live it all come back on for 2 poxy minutes then it would come back on .I had to leave disconnected and will be returning back tommorow . Any suggestions would be extremely grateful
Thanks
I was at a Job earlier today,the customers upstairs lights would not turn on due to the 6A mcb operating so it's a short circuit so I disconnected the supply to the first light the supply disconnected from consumer unit ,then did a insulation resistance which came out clear tried the mcb without any connection it stayed on.so connected the supply at consumer unit and left the other end not connected to anything it stayed on so connected the loop out and switch live it all come back on for 2 poxy minutes then it would come back on .I had to leave disconnected and will be returning back tommorow . Any suggestions would be extremely grateful