Dear All
Thanks for everyoned
Dear All
Prize goes to Midwest
It was load for some reason. Unplug everything and all’s well
Nothing in particular stopped the test but the combination did. Not sure I get it but I’m testing the installation so all good
Can I have a pint now westward ??
Hi Risteard
I thought of faulty rid but to have two , one single socket one double would be very odd. I rang timeguard and they said it was possible so am getting two more from wholesaler but don’t expect it to cure it
To be honest I was expecting someone to rip me a new one and say I’d missed...
Dear All
Installation tncs. Wyler re-wireable fuses
I’ve fitted 2 x timeguard rcd sockets to provide protection for extension leads going outside but neither will trip with my tester. Trip fine on test button
Also trip when I do earth loop test ( fluke tester)
Socket tester says it’s all ok
Zs...