Dear All
Installation tncs. Wyler re-wireable fuses
I’ve fitted 2 x timeguard rcd sockets to provide protection for extension leads going outside but neither will trip with my tester. Trip fine on test button
Also trip when I do earth loop test ( fluke tester)
Socket tester says it’s all ok
Zs before I changed to rcd socket was 0.45
Doesn’t trip on ramp test
Ze 0.21
What the hell am I missing

Advise appreciated
Cheers
 
I've come across faulty SRCDs out of the box before. Obviously without having seen the installation I can't say that this is the case here but certainly it is possible.
 
I've come across faulty SRCDs out of the box before. Obviously without having seen the installation I can't say that this is the case here but certainly it is possible.
Hi Risteard
I thought of faulty rid but to have two , one single socket one double would be very odd. I rang timeguard and they said it was possible so am getting two more from wholesaler but don’t expect it to cure it
To be honest I was expecting someone to rip me a new one and say I’d missed something obvious
 
Agree with Strima, think you may have an IR fault. Have you done that test? Had similar experiences before, RCD not tripping & RCD tripping on Zs test. Both done to IR fault, neutral earth. That said, that was RCD at origin of circuit, but worth considering.
 
are they passive or active rcd sockets?
I had an issue testing rcd sockets before now, they were passive ones, simply didnt always trip on a 1 or 5 x test. They were passive ones, they were a new generic unbranded model out at the time and cheap nasty stuff from far east. I took them back for a refund and turns out they later got recalled as the passive circuitry inside was no good.
I have heard that passive as opposed to active rcd sockets can cause issues with testing as they have the reset part built in.
 
are they passive or active rcd sockets?
I had an issue testing rcd sockets before now, they were passive ones, simply didnt always trip on a 1 or 5 x test. They were passive ones, they were a new generic unbranded model out at the time and cheap nasty stuff from far east. I took them back for a refund and turns out they later got recalled as the passive circuitry inside was no good.
I have heard that passive as opposed to active rcd sockets can cause issues with testing as they have the reset part built in.
These are timeguard active ones. I wondered if they need a ‘special ‘test but apparently not
 

Reply to Timeguard rcd socket won’t trip with tester. Help please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top