Guys, don't get sidetracked into the same old VO conversations - I think we all know our opinions on those (at least in a domestic environment anyway), this PV+ unit is pitched as something different....I for one would like to know exactly how this is supposed to differ from VO and how it's...
It's a Matt:e product and I'm sure it has its place, but if you're not suffering from regular over voltage trips then I fail to grasp the point....seems like a solution to a problem that shouldn't exist...I've questioned the ER grid-connection compliance/impact of this technology before, but as...
But then, they are hardly going to completely revamp the "FiT" banding structure, hence why there are two questions to answer "no" to in their wording above....which kinda makes sense then - don't affect the banding, and don't affect the here ration capacity, and you're ok?
Gavin - perhaps Ofgem are wording it as generation capacity because they are finally seeing the sense of ignoring the amount of watts-peak installed on the DC side?.....or am I giving them too much credit?
Indeed Ted, this ongoing saga with TIC/DNC definitions and restrictions is continuing to be a pain in the proverbial. I'm seeing similar inconsistencies and poor consideration/wording with recent export limitation policy from various DNOs too, although it has to be said that they are all pretty...
First thing, I'll reiterate what several others have already said - for transformerless inverters, always try to "design-out" or mitigate the requirement for an RCD in the first place.
All transformerless inverters will have a degree of inherent leakage current. I think that G83/2 requires...
Assuming you tested the strings whilst open-circuit, did you monitor the "on-load" voltage and current values reported by the inverters too? Just curious as sometimes panels can behave differently when actually outputting current. Shading is most likely to be the culprit though tbh. Unless...
Completely agree, I believe discussions with DNOs are ongoing, but it certainly seems that some of them are considering some systems as adding generation capacity, for some strange reason. Maybe it will become clearer/more sensible soon