How is 0.2s disconnection time met on TT? | on ElectriciansForums

Discuss How is 0.2s disconnection time met on TT? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Joined
May 12, 2019
Messages
193
Reaction score
39
Location
London
Hi all, studying for 2391 and confused on disconnections times for TT systems

Now I’m comfortable understanding the disconnection times for TN systems that need to be met which is 0.4s and because the Zs will be low enough to cause a high Ipf to cause the MCB to operate within 0.4s… also from Rcd/RCBO which disconnects in 300ms (0.3s)

But what I’m baffled on is for a TT system. The Ze will be too high which will make the Zs too high also and will not meet max Zs for the MCBs which is why RCD protection is required… but if the max disconnection is 0.2s type A Rcd/RCBO will not meet the disconnection times. Spoke to a friend and he said 100ma type S RCD which has a disconnection time of 200ms but then that will disconnect before all the rcd /rcbos meaning the rcd/rcbos will be pointless and the S type will cause all to trip at the same time??

How do you achieve separation of circuits to avoid nuisance tripping?

Please correct me if I’m wrong and help me get my confused brain around this.

Thanks
 
Hi all, studying for 2391 and confused on disconnections times for TT systems

Now I’m comfortable understanding the disconnection times for TN systems that need to be met which is 0.4s and because the Zs will be low enough to cause a high Ipf to cause the MCB to operate within 0.4s… also from Rcd/RCBO which disconnects in 300ms (0.3s)

But what I’m baffled on is for a TT system. The Ze will be too high which will make the Zs too high also and will not meet max Zs for the MCBs which is why RCD protection is required… but if the max disconnection is 0.2s type A Rcd/RCBO will not meet the disconnection times. Spoke to a friend and he said 100ma type S RCD which has a disconnection time of 200ms but then that will disconnect before all the rcd /rcbos meaning the rcd/rcbos will be pointless and the S type will cause all to trip at the same time??

How do you achieve separation of circuits to avoid nuisance tripping?

Please correct me if I’m wrong and help me get my confused brain around this.

Thanks
The reality is that it won't only be the minimal operating current in a fault, and even if there is 2 I delta n flowing then disconnection times will be much quicker. Of course we don't actually carry out a 2 I delta n test (or even need to do a 5 I delta n test anymore).
 
Upvote 0
The reality is that it won't only be the minimal operating current in a fault, and even if there is 2 I delta n flowing then disconnection times will be much quicker. Of course we don't actually carry out a 2 I delta n test (or even need to do a 5 I delta n test anymore).
Your reply has confused me more if I’m being honest… the minimal operating current of the Rcd i.e 30ma/100ma? And what is 2 I delta n? Is that 2x the rated tripping current of the Rcd? Delta being the triangular symbol?

So how would we confirm that 0.2s would be met by selecting the right RCD for TT? What I’m struggling to understand is how to get around the nuisance tripping of all circuits…

S type 100ma will trip in 0.2s which is good but will cause all other circuits that it serves to be knocked out. 30ma rcbos will realistically trip within 0.2s too but they’re designed to trip within 0.3s so they can’t be selected…
 
Upvote 0
30mA trip current would trip up to 7666 ohms on 230v.
100mA would require 2300 ohms. Anything above 200 ohms should be considered unstable.

100mA is there for fault protection, that is line - neutral faults.
 
Upvote 0
30mA trip current would trip up to 7666 ohms on 230v.
100mA would require 2300 ohms. Anything above 200 ohms should be considered unstable.

100mA is there for fault protection, that is line - neutral faults.
I did some digging around on some forums last night and managed to work it out and it made sense to me what you meant on your first reply…

Correct me if I’m wrong…

So 0.2s disconnection time is for fault protection and when using type A/Ac Rcd then providing that the Ze is low enough you will get a fault current high enough to trip the Rcd at 0.2s…

Rcd tripping at 1x tripping current is 30ma which should trip within 300ms which wouldn’t comply with the 0.2s even though most likely it probably will trip within that time…

But Rcd tripping at 5x the tripping current should trip within 40ms/0.04s which will meet the 0.2s required disconnection times and as the fault current will be more than 0.15A/150ma it will trip within 0.04s.

So if all circuits are on Rcd/rcbo then no need for S type Rcd

If there are some on Rcd/RCBO and the other circuits don’t require additional protection ie distribution circuit or cooker circuit 40amp but they require fault protection providing it meets the requirements not to be on additional protection then a up front S type RCD time delayed Rcd set to 500ms would be fine as the disconnection time will need to be 1s as stated in 411.3.2.4
 
Upvote 0
The 100mA RCD is for fault protection. The 30mA is for additional protection.

TT systems have a 1 second disconnection time for fault protection.
0.2 seconds for earth fault protection.
The reason for time delayed is to give time for 'local' disconnection.
That is my understanding of it though I may not be 100% right.
 
Upvote 0
The 100mA RCD is for fault protection. The 30mA is for additional protection.

TT systems have a 1 second disconnection time for fault protection.
0.2 seconds for earth fault protection.
The reason for time delayed is to give time for 'local' disconnection.
That is my understanding of it though I may not be 100% right.
Okay thank you this makes sense…

Was I right about how to meet the 0.2disconnection time?
The EFLI on TT being low enough to have a high enough earth fault current which will trip the Rcd at 5x the tripping current which will cause it to trip at no more than 40ms which meets the 0.2s requirement
 
Upvote 0

Reply to How is 0.2s disconnection time met on TT? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
697

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top