    I really want it but I can't justify spending £25 on it when it's gonna get updated before I actually need it! I've been thinking I should just bite the bullet, but I remember a thread on here not long ago about dodgy copies from amazon. Was my answer OK then?
  2. F

    Real Life Customer Enquirer

    R1+R2 for all earthed points on all circuits, check bonding on all extraneous conductive parts (continuity not above 0.05Ω). If lighting circuits are unearthed I would be tempted to ensure no fittings requiring an earth are present, although this is more in the scope of an ECIR.
  3. F

    Real Life Customer Enquirer

    Global IR, good chance on an installation of this age the insulation of the cables has degraded to the point there is a high impedance fault between L/N and E. If you don't confirm the IR values are acceptable, the newly added RCD is may trip and you will have an understandably unhappy customer...
  4. F

    Real Life Customer Enquirer

    I'm shooting in the dark with my lack of knowledge here, but although this work wouldn't count as a complete rewire, wouldn't it be bad practice to relocate the CU in an inaccessible location? Another under counter cupboard away from the sink would reduce the risk of water of water intrusion...
  5. F

    I'll start this week's

    Very late to the party here but a few points I wanted to make. Those calling for tougher sentences, that has been the policy for the last 50 odd years, what has the end result been? Greater demand, greater supply, decreases in price, criminalisation of non violent users, £Trillions into the...
  6. F

    #*#*# free prize for a post #*#*#*#*

    I've already won a multimeter, I'll let someone else win the next prize!
  7. F

    #*#*# free prize for a post #*#*#*#*

    I don't want to be entered into the comp, I've already done well enough from the trainee section! Just wanted to say thanks again to all those involved, moderators and mentors for your generosity, time and the knowledge you share. Also to trainees for asking questions I find interesting! No...
  8. F

    do I need an earth stake - metre is 25m from fuesboard

    :6:What a doughnut! I usually spot these a mile away, just this time it's on a subject I'm a little unfamiliar with. At least now cairns doesn't have to ask the same question!
  9. F

    do I need an earth stake - metre is 25m from fuesboard

    Could someone explain to a trainee why it would be lethal to use the DNO supplied earth in such a situation? If you installed a 30ma RCD at the service head and then another in the DB surely you haven't accounted for discrimination.
  10. F

    Agencies and payroll

    Having worked for several agencies, each with a diffrent payroll company, my assumption is their must be some type of a referral fee paid to the agency. Once I had a month between jobs for the same agency, they made me sign up to a different payroll, refusing to allow me to use the previous one.
  11. F

    Barn raising

    My solution: 1. Buy a large quantity of solar tiles. 2. Sell to Armish at fraction of the price as super insulated fire retardant roofing tiles. 3. Explain that due to metal construction they pose a higher risk of lightning strike, sets of tiles need to be linked by 'lightning tube'? (call it...
  12. F

    Barn raising

    Like a colony of bearded ants! Pity they will never need our trade.
  13. F

    Thanks Paul!

    I've got a long way to go to get to your level of kindness Paul! The voltstick is unopened and waiting for the next comp to end, if the winner doesn't mind a possible continuation of the joke name gag... I hope the multimeter comes with another, it makes waiting for the package that bit more...
  14. F

    Thanks Paul!

    I'm more than happy to post the volt stick to the winner on the next comp mate, you don't have to worry about footing the bill for another. I'm grateful enough to have the multimeter!
  15. F

    Thanks Paul!

    Unless I'm going seriously blind and/or demented it's definitely a volt stick. My sanity could always use a second opinion though (well 5th if you count the voices in my head).
  16. F

    Thanks Paul!

    Didn't get to see the postie sadly. I wasn't looking forward to getting a slip, then heading to the sorting office to convince someone I was in fact Flexible Mick! I think I may have got the wrong package though, it has a Megger volt stick in it. Thanks again mate, all the best.
  17. F

    ** Winner for the Ceiling Rose Challenge is.....**

    Oops! Must have been because I feel so at home here I didn't think a name would be necessary... Yea I deserve it, all part of being a trainee. Do your worst!
  18. F

    ** Winner for the Ceiling Rose Challenge is.....**

    Wow, I really didn't expect this, after seeing the show us your installs thread I was just happy to put a picture up in a thread where the workmanship didn't pail in insignificance to the rest. I'm still a long way off completing work of that complexity and standard, but it's nice to have my...
  19. F

    The ceiling rose challenge!

    Thanks for the comments, it was really satisfying taking the time to do it as neat as possible. Now all I need to do is find someone who's willing to pay me to spend that long second fixing.... I've had to change a few fixings with bugger all slack in the cables, and vowed to never inflict the...
  20. F

    The ceiling rose challenge!

    My attempt: Took far longer than I would like to admit!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top