There's a few more pre change tests to be carried out too. Well at least I do em.

Global IR, good chance on an installation of this age the insulation of the cables has degraded to the point there is a high impedance fault between L/N and E. If you don't confirm the IR values are acceptable, the newly added RCD is may trip and you will have an understandably unhappy customer!

Also Ze to check the earth supplied to the property is acceptable?
 
Global IR, good chance on an installation of this age the insulation of the cables has degraded to the point there is a high impedance fault between L/N and E. If you don't confirm the IR values are acceptable, the newly added RCD is may trip and you will have an understandably unhappy customer!

Also Ze to check the earth supplied to the property is acceptable?

And?? a bit more regarding earthing
 
R1+R2 for all earthed points on all circuits, check bonding on all extraneous conductive parts (continuity not above 0.05Ω).

If lighting circuits are unearthed I would be tempted to ensure no fittings requiring an earth are present, although this is more in the scope of an ECIR.
 
R1+R2 for all earthed points on all circuits, check bonding on all extraneous conductive parts (continuity not above 0.05Ω).

If lighting circuits are unearthed I would be tempted to ensure no fittings requiring an earth are present, although this is more in the scope of an ECIR.

Have you been reading GN3???? LOL your 0.05ohms that referring to the https://www.youtube.com/watch?v=v38PfIVy2rIextraneous parts is it? https://www.youtube.com/watch?v=rnvNfI__kYU
Check these out
 
Last edited:
I really want it but I can't justify spending ÂŁ25 on it when it's gonna get updated before I actually need it!

I've been thinking I should just bite the bullet, but I remember a thread on here not long ago about dodgy copies from amazon.

Was my answer OK then?
 
I really want it but I can't justify spending ÂŁ25 on it when it's gonna get updated before I actually need it!

I've been thinking I should just bite the bullet, but I remember a thread on here not long ago about dodgy copies from amazon.

Was my answer OK then?
I think your 0.05 ohms is referring to the main protective bonding conductors, check out the two vids I sent you that will clear up your answer I hope. The figure for extraneous metalwork is 2200 ohms or 0.02 megohms, the vids will explain better that I can
 
Last edited:

Reply to Real Life Customer Enquirer in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top