I'm just the tester on the job. I still have't seen the switch rooms. I'm guessing that these are existing breakers at their lowest settings.. I'm just used to seeing a breaker at the origin that would protect the cable. I'm asking will they disconnect under fault conditions. I'm not sure the...
Hello engineers.
I have a query. I have a panel board(mccbs) containing 100amp mccbs supplying various "life safety DBs" lifts, water mist pumps etc.The panel board has an MCCB of 250 AMP as the main switch. It is supplied from an ATS in 120mm sq.4 core with 70mm earth.A run of 20m.The ATS is...
The increase in loop impedance from. 0.20 at the DB to 0.79 on a 10m run sounds like something not right ,loose connection ?As another poster suggested. Try testing with probes at the socket terminals. But having the RCD ..it will be fine. ..⌛
No update yet then?. If it's a flat that was devided up from the main house at one stage.Maybe you are on someone else's supply.. Yippee free lecky.Is everything else in the house off when the main switch goes off?
No doubt I'm missing something here but the ones I've done, are switched from the surgeons panel and just come on at the same time as the socket, not on the control circuit. I don't think there is a requirement to provide a fail safe mechanism. A buzzer might be a better warning than a lamp.
Hi
I have a testing job to do in ireland.The test sheets i've to use ask for the R2 reading only..not R1+R2.....It is impractical to use the long wander lead method so I was thinking to work it out from R1+R2-(R1+Rn)/2=R2.........I was thinking to use this as opposed to R1+R2/2 to take account...
There are other concerns too..maybe there could be another radial in the kitchen with a 'lost ' earth and the previous spark has already borrowed the cooker earth......So new cooker circuit in /old cooker circuit out might leave another circuit unprotected...Full test might identify that..I...
Presuming that the plug is now removed...it is up to the landlord to ensure the installation is safe for the next tennant as he is required to have the place inspected/tested
Hi Peter
I haven't read all of the posts on here so please excuse if this has been covered already.
I'm fairly sure it is indeed a legal requirement on change of user to have inspection carried out.
The code should be C3 for no rcd for socket outlets.C3 for no rcd on bathroom circuits and C3 for...
And leave the rest NOT covered? Surely bathroom lights have been reqd to have rcds for at least 10 years and the rest needs it for cables buried in walls
And leave the rest NOT covered? Surely bathroom lights have been reqd to have rcds for at least 10 years and the rest needs it for cables buried in walls
14kw sounds really big cooker for a private house...housing association?Is it an HMO? If so it may not necessarily be considered as domestic as there could be more than one person cooking at once so your normal allowable diversity of first 10 amps plus 30% of the remainder wouldn't be...