  1. markythesparky

    Ring main.

    How do you know they are both rings? Have you tested them? 1592598367 Appendix 15, page 505. 1592598620 Beg to differ; appendix 15, page 506.
  2. markythesparky

    Ze=1.87 TT or TN-S?

    Just out of interest, why are you doing a no trip test? Suppliers don’t give the consumer RCD’s.
  3. markythesparky

    No load fuse trip but not RCD.

    This is what happens when someone who is not qualified to do the work does the work! Yes, any electrician who is a real and proper electrician (Not someone who says they are) should have and be able to use the relevant testing equipment. If he/ she does not have it then it is not worth them...
  4. markythesparky

    Help!!! Can't turn electric off!!!

    Believe or not the brown tail is the neutral by the looks of it. Incredible! The grey tail is the TN-C-S link between earth and Neutral even though it is also set up as a TN-S. I’ve seen this twice before.
  5. markythesparky

    Adding circuits to a full DB

    Please elaborate....
  6. markythesparky

    Need help/advice, insure of what the problem is and think I’m being ripped off

    If he's not got a insulation resistance tester then he is not an electrician worth employing. If hes undone all his work and cannot find the problem visually then, to be fair to him, it may not be his work, it may be a coincidence. That said, if he has a IR tester the next procedure is to...
  7. markythesparky

    Adding circuits to a full DB

    There seems to be a marked difference in opinion on this thread than another similar one that I had argued before : (Does this setup contravene any regs or is it ok? - https://www.electriciansforums.co.uk/threads/does-this-setup-contravene-any-regs-or-is-it-ok.167990/. For the record, and you...
  8. markythesparky

    Currys refused to install my daughter's cooker, but....

    What was it 117v between and what did you get 240v between?
  9. markythesparky

    TOES abbreviation of

    Can you give us a photo of the actual EICR where’s this is mentioned? It may help.
  10. markythesparky

    Can't reset the RCD with any MCB's on - Faulty RCD?

    Yes that’s possible with that fuseboard although if your electrician has changed that rcd, it doesn’t comply with regulations. There are regulations regarding discrimination which your installation falls short of. He/ she should not have issues certs staying that it complies. However, getting...
  11. markythesparky

    Can't reset the RCD with any MCB's on - Faulty RCD?

    What was there before the new rcd was fitted? Was it a straight forward main switch?
  12. markythesparky

    Is this NICIEC extractor fan installation safe?

    If this guy or madam is a qualified electrician, I will be a monkeys uncle and if you get a properly filled out certificate, I will eat my hat!
  13. markythesparky

    Shed supply from new build property

    Correct. It should be a serious consideration. This is why you are not allowed PME for the new EV chargers.
  14. markythesparky

    Where are CCTV notices required?

    What about if the camera picks up a crash on the public highway that has damaged the cctv owners car as it was parked outside on the street?
  15. markythesparky

    Shed supply from new build property

    Exporting PME is not a good idea, especially if the floor of the shed is not insulated.
  16. markythesparky

    Where are CCTV notices required?

    To be honest, I struggle with that on a normal Friday night out!
  17. markythesparky

    Knob & Tube question

    I’ve seen quite a few of these doing electrical work in the UK. They were more active during the mid 2000’s but slowly but surely they are being eradicated. They offered a serious risk to home grown, qualified, UK sparks and it’s good to see that since the rise in knowledge from the UK...
  18. markythesparky

    Shed supply from new build property

    Being a new build, I would have thought this would be a TN-C-S. As such do the builders know if the shed has a wooden floor or have they even asked?
  19. markythesparky

    Where are CCTV notices required?

    Blimey! What a mine field. What about if somebody has CCTV, a break in or damage occurs. Can the recorded footage be used to prosecute even though no signs were present?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top