  1. MFS Electrical

    UK Relevance of Table 41.3 where Additional Protection is present?

    If I encountered this on an EICR I’d still code it as a C3. It is technically compliant, however the Zs exceeding the MCB type and rating is just bad design. Having said that I’ve rectified many a C2 for high Zs by changing to an RCBO. Would the loads allow for a reduction to a C20?
  2. MFS Electrical

    UK What should I charge to install a EV charger

    Don’t Forget the DNO notification forms too
  3. MFS Electrical

    External lighting around perimeter of Sports Complex

    I’m with you on that, protect with an RCD. Gives Fault protection as well and additional protection and ensures it will disconnect up to 1667ohms. I’d also write in your EICR that you recommend more frequent inspection interval on the floodlighting as the fault protection is relying on the...
  4. MFS Electrical

    Rewiring Attic in Edinburgh

    In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a warrant...
  5. IMG_8599.png

    IMG_8599.png

  6. MFS Electrical

    Rewiring Attic in Edinburgh

    You’ll need a building warrant if you’re planning to rewire a flat in Scotland. That could be very tricky if you don’t have Scottish/UK qualifications. Beware of derating the current carrying capacity of cables when putting them in conduit or trunking, you may find that they are already...
  7. MFS Electrical

    UK SJIB ECS card grading for 2391-52 (equivalent)

    My older card has it but my newer card doesn’t
  8. IMG_7669.jpeg

    IMG_7669.jpeg

  9. IMG_7670.jpeg

    IMG_7670.jpeg

  10. MFS Electrical

    BS7671 Section 740 ADS via OCPD Query

    Spot on The Requirements of sections 1-6 must be complied with in a special location unless its otherwise stated in that part of section 7 that a specific requirement of section 1-6 is not applicable. In basic terms you could say that Section 7 contains additional requirements or...
  11. MFS Electrical

    Section 7 checklists

    I reckon you could @Dan I think the best way to record the additional inspections would be an inspection checklist similar to that as found in an EICR but one for each Section 7 location.
  12. MFS Electrical

    Section 7 checklists

    When doing an EICR on something like a swimming pool there is a section on the inspection checklist which asks about any other special locations and asks to record the results of the inspection separately. My question is are there any templates for inspections for special locations (especially...
  13. MFS Electrical

    3 phase problem after spark did 5 year safety inspection

    So he didn’t remove the tails? But wiggled them? Sounds more likely that there’s been a problem hiding there for a while either from a loose connection causing the cable to overheat and eventually melt into the clamp or the wiggle has exacerbated a defect already there and with a little load on...
  14. MFS Electrical

    3 phase problem after spark did 5 year safety inspection

    Certainly not a standard thing to do on an inspection. When you do the 2391 (inspection and testing) you are told to disturb as little connections as possible to ensure you don’t create faults. It’s highly unlikely that the electrician would have removed the tails and reterminated them on an...
  15. MFS Electrical

    UK Can anyone tell me what is wrong/incorrect.

    Still not done properly though, pretty bad practice earthing the armour from the far end of the circuit. Zs of the braid would be significantly higher. And installed contrary to manufacturer’s instructions.
  16. MFS Electrical

    UK Can anyone tell me what is wrong/incorrect.

    According to NICEIC and Select it isn’t classed as a suitable enclosure as non-skilled persons access the enclosure regularly/to read the meter etc.
  17. MFS Electrical

    UK Can anyone tell me what is wrong/incorrect.

    Things wrong in this picture; 1. Basic insulation showing (meter cabs are not considered suitable enclosures) interestingly site applied insulation (heat shrink) is no longer classed as suitable in an application like this either. 2. Black being used as the N (personally don’t see a problem...
  18. MFS Electrical

    Lucien Nunes Electrical Engineer Extraordinaire

    I really do hope that MEET comes to something. What a fantastic concept.
  19. MFS Electrical

    Lucien Nunes funeral (celebration of life) details......

    I'm sorry to hear that Lucien has passed. Please pass on my condolences to the family. He will be missed on here.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top