Recently did an EICR on external lighting, installed in the early 70’s, never been tested before & never compliant.
The Swa’s are 2.5 x2 core entering in a recently new Cut Out.
The problem the Client as now is that @ least 4 lighting points have high Zs reading over 10 ohms.
Installing new Swa to these positions are gonna be problematic.
The easier option if possible would be to protect these 4 light points with a 30 ma Rcd, rather a Temporary fix @ this moment.
Or disconnection of these lights not gonna be popular there.
Any ideas my comrades