Good maths, but why are you telling me about the maximum lengths of cables in regard to voltage drop, when the question is concerning maximum Zs values?
In BS7671 Table 41.3, page 58 states:
The Zs for a 32A type B CB to trip in 0.4s is 1.37 ohms
The On-Site-Guide, Table B6, page 125 states:
The Zs for a 32A type B CB to trip in 0.4s is 1.1 ohms
Is this the table that is wrong?
Thank you, that is the table I was looking for. So that was the table that came with my OSG. I have two copies of the OSG and I have lost the correction table from both :(
They do not make that table easy to find do they. Thank you!
Hi I am training to become an electrician. I am just putting this out there for some more experienced electricians to maybe comment on.
The op said the switch controls a florescent tube, could it be that, it is the inductor in the tube causing the RCD to trip. I am wondering if it has...
Can anyone help me understand Zs values.
In the On-Site-Guide page 60 Table 7.1 under the heading Maximum cable length, it states if
Zs < 0.35 ohms for a TN-C-S system
you can have a cable length of 107m
In BS7671 page 58 Table 41.3 it states the
Maximum Zs for a 32A CB to operate within...
I just do not understand :(
I kind of understand, I think, The larger the CSA of a conductor the less the resistance.
So are you saying that I have to treat the entire earth as its CSA?
If so then it all makes slightly more sense to me.
Thank you.
I do understand that people do get killed by electricity, I just didn't understand why.
So is it because we our systems that causes the lethal situation?
you say the resistance between your body and earth. But the current still has to get back to the transformer. Why have you not factored in the resistance of the earth to the transformer?
If i am on the 2nd floor or in a loft, how can I get much of a shock? The resistance path is through my body, through the building structure then through the earth to the transformer. That is a massive resistance
well wikipedia says resistance of the soil is between 10 - 1000 ohms per meter, so lets say 500 ohms, smack in the middle.
Say the transformer is 100 meters away. Ohms law current = volts / resistance,
so 500 ohms x 100 meters = 50,000 ohms.
I = 230 / 50,000 = 0.0046A
0.0046 amps is not much...
Hi I am studying to become an electrician.
There are a few things I do not fully understand regarding shocks and earth and I cannot find the answers to some of my questions.
Can anyone help me understand the following points regarding a standard TN system.
1) If you are in a loft or a 2nd...
Previous posts must be right, I must be using the wrong value for (t)
I read this chart as saying I should use the value 0.01
Other posts say I should use 0.1
I don't see why
The current is well over 200A, at which point the breaker would trip in 0.01s ???????????????
I agree the final S value does not seam right, because 6mm cable has a 2.5mm CPC. You should be able to use a smaller CSA conductor than what is recommended, or at least the same. I can't see where I went wrong tho :(