In is the rated current or current setting of protective device, so that would be 40A BS EN 60898. Therefore your tabulated calculation is slightly off as it uses 37A as opposed to 40A. You could use Ib in this calculation if overload protection was NOT required.

The picture highlighting your first R1+R2 values also show 6mm plus 2mm, however your calculations take the values of 6mm and 4mm.

The final calculation for your S value also does not quite add up either.


I agree the final S value does not seam right, because 6mm cable has a 2.5mm CPC. You should be able to use a smaller CSA conductor than what is recommended, or at least the same. I can't see where I went wrong tho :(
 
I believe you'd use the 0.1 value for t, giving a more "worse case scenario" and at those times you really can't split it down anymore from the information you've been given. However having recently done this I was told that you can do a super ultra worse case scenario and plug the value of 200A in as your current in relation to the corresponding t value, if your cpc complies there then you can't go far wrong.

Using 200A and 0.1 for the and 115 for k - you get 0.54mm2 so it proves your choice of cables comply
 
I read this chart as saying I should use the value 0.01
You can't use the generic tables for 0.01 second disconnection - as I stated earlier this is the definite minimum operating time but requires the manufacturer's data (which you will note is stated at the bottom of that table). So you need to know what brand of device you are using and consult manufacturer's data before using a disconnection time of 0.01 seconds - although with a sufficient fault current it is likely this will be achieved and therefore 0.1 seconds would be unduly pessimistic.
 
You don't have to use the BS7671 generic data. If you have the manufacturer's data for the device you are using then that is what you should use for a more realistic result.

Hi, yes you are right, but with regards to the op 0.1 is correct. Just a note, you shouldnt use graphs for disconnection times below 0.1, the are not reliable, use the documented KA2S
 

Reply to Help with CPC size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top