Highlighted in the red above you say from the Zs/Zdb to get the ipf you go straight to the rcd testing this is not correct as you need to do the circuit Zs on thecircuits you dont have to takeapart to do this (all ones you have to expose live parts on canbe calculated) like the socketcircuit you...
Hi Ian is correct on the AM2 the college wont let you test between phases and you need to just use the rule of thumb and double it.
I dont think it is a fact that they are not capable of doing the test as when i did my AM2 i was more than capable but the college just dont want you to do it, i...
Why would you disconnect the cpc any way that is not connected into the rcbo just take out the line and neutrals and remove fly leads and sorted i would say.
It is stated all cpc need to be connected when testing ir so dont remove any cpc at all
I was going to state what is above aswell. Are you testing at the switch side of the celing rose? Not the loop in the middle? Also have you checked the continuity of the flex drop aswell as there may be a loose wire in the drop its self and are you sure the drop is not damaged. Try changing it.
To be honest mate if that is the only thing they lie on its not to bad. I was at my sister's before just on the computer with my nephew and her landlord sent a sparky round to do a eicr and he was there maby 40 minutes and it was suppose to be a 100% test and inspect and there was no way he...
Aslog as it makes a good connection and is done correctly probily not. That been said a friend of mine failed his install part of the am2 due to using 1mm fly leads on the metal back boxes so who knows.
I have seen this set up quite alot in the local housing association jobs. 2.5 t+e from 16A breaker to the supply side of the fused spur then from there down to a socket. Then 1.5 t+e from the load side of the fused spur to a pendant and a 5A fuse fitted in the fused spur all usually in conduit...
Haha yeah thats is a good way to do it. But i bet most of us still say bulb when actually on about a lamp. I made the mistake and said it to my missus before "get a lamp for the spare room while your out" and she actually came back with a plug in lamp and said why not just get a bulb it would of...
Use a wander lead and test to the water pipe to the bonding conductor in the board if it is less that 0.05 ohms then i would say its fine and just note down that the clamp is inacessable to view or check.
Also agree with tel above 0.05 is not the cable its to the pipe it is connected to as you...
Just put a bit extra on your cv nothing massive or any thig that you cant do just say you have had 6 month experiance 2nd fixing or something simple like that every one embellishes a bit on there cv.
I would personally just take all the line/live out of the fused spur and connected them in the back with a wago thats how i did it but i suppose the way you describe would be fine aswell.
When the board is live you are allowed to take the cover off it that does not necessarily expose live...
When doing the ir test on the sockets just take the live out of the fuse spur and link it with wago in the back of the box to the live on the load side of the fuse spur as then you will test the full circuit as if you just turn it off or take the fuse out you will only be testing part of the...
The best way mate is to look for electricians mate work, do you have a cscs card? If you keep sending your cv off to company's you will find something I use to send my cv off to nearly 100 company's a month at first to try and get some thing and it worked when I first started in the trade to try...
The testers they used in my AM2 did not allow phase to phase testing so yes you just do line to neutral on all 3 lines and double the highest value and then line to earth on all 3 lines then which ever is higher (more than likely one of your pscc) put that down as your pfc.
Just relax mate when...
When you go into the AM2 the first thing you have to practically do is safely isolate the board but you still have power to the board on the incoming tails so you can still do the Ze test then add your R1+R2 to that to get your Zs.
There is a few ways you can test the motor you either test the...
What reg stated it needs to be between 1350 and 1450? I'm not saying your wrong I just did not know of this reg, I know they have to be accessible so obviously the loft us a very bad place.