My money is on this possibility or something similar. For instance, we have recently had to carry out testing on premises that were dormant/vacant for 2 years (covid related). A number of FLi socket circuit tests were marginally higher than the regs allowed. I did wonder why the installation had...
By "main earth" you are probably referring to the earth going to the rod?? Australia has a TNC-S system. That means you can end up with current flowing in any bonded metalwork because its connected directly to the neutral. You won't get any current (nothing measurable anyway) flowing to earth...
Can I ask how much "additional cost" comes to in euro, s and what particular brand caught your eye.? I also want to get one with the capacity for measuring DC leakage
I support that conclusion 100%.I also comepletly understand the reticence of the other posters. Afterall the message that wall switches in bathrooms place the user in mortal danger continues to be preached to every electrical apprentice from day one. That's the same apprentice who will travel...
I suspect there is, nt anything "wrong" per say. Inrush current is a feature of every electrical circuit. The natural leakage built in to the appliances you are using will also experience a momentary spike when initially plugged in. Usually rcd, s can cope with this but in your case there is...
Never. First observation is that it's unlikely it was installed by a conventionally trained electrician.A cooker should have its own circuit. Most countries would require it (can, t speak for UK) And if it is allowed, it is terribly poor design.
. Next obvious question is... Is it...
Correct. And it's likely from your description that all is in fact in order. You are getting readings currently that are confusing for you, which is understandable. To "unconfuse" the situation bear in mind that what you are there to actually test is the "fixed wiring". In principle this means...
You have 50% of your solution right there. I would be keeping my IR tester in its box and first determine exactly what's on that circuit that might be affected by rain. Its usually something exposed to the elements. As a general rule you want to disconnect as little as possible during...
Firstly the "differential" (rcd) will only trip when's its rated leakage current is exceeded (30 ma). Any appliance which has intentional leakage in its design will "spark" if you disconnect or reconnect its circuit CPC but will not trip the rcd as the intentional leakage is designed to be...
1 Meg is actually allowable. The problem is that it is highly unusual to get a reading like that in the fixed wiring of a standard installation. It's highly likely that there is something connected in circuit that's dragging down the reading. And until you find out what it is, it can be vexing
There is almost certainly leakage from live to earth. But what kind of leakage is it? Intentional or unintentional?
If it was a socket circuit I would regard your issue, s as nothing unusual. Remove the CPC from your average ring circuit and you will almost certainly measure a significant...
No. Your marbles are very much where they are meant to be. But if I may offer my final comment on this post, it's this. Bonding as a topic is the "gift that keeps on giving" from the point of view that since I, ve been an apprentice no other single electrical subject has caused me more "head...
Won't download for me. What's the doc called?. I can Google it
If simultaneousely accessible and class 1 accessories are used then that changes the scenario significantly. But I understand that previous posts established that the metal posts were not simultaneousely accessible.
So which of the above figures would be regarded as the cut off point for when something is regarded as extraneous?. There is quite a gap between 7.67 and 22 Kohm.