  1. L

    Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.

    This will be my last post on this First time we were called to fault with storage heater there was a live to earth fault on the existing cable fed from E7 consumer unit on a 16 amp 60898 MCB I’m not sure what the installation resistance was I didn’t go Deakon ran a new 2.5 cable to heater...
  2. L

    Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.

    Turn of events for 5 visits 1 visit Call out storage heater not working Tested storage heater and circuit found to be fault with circuit live to earth dead short (Electrician 1) 2 visit Install new supply to existing storage heater (Deakon) Storage heater worked for 4 days 3 visit...
  3. L

    Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.

    Fault found Fault is with BSEN60947-3 100amp main switch arcing live conductor While testing incoming voltage with multimeter I had clamp meter on out going supply Voltage fluctuating between 235v and 210v resulting in outgoing supply to heater going up and down between 13 and 16amp...
  4. 285CCF86-C7E7-43B5-B329-0C90C241D9E3.jpeg

    285CCF86-C7E7-43B5-B329-0C90C241D9E3.jpeg

  5. L

    Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.

    I am going tomorrow at 6am I will let you know my findings
  6. L

    Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.

    His name is on top of his post are you TWP Boyfriend how old are you grow up Yes I know Deakon he told me about the problem He is a young chap trying his best its not 5 sparks it he’s been back 5 different times trying to solve problem and one other has been He doesn’t need clowns like you...
  7. L

    Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit.

    I have Never heard so much nonsense in 20 years of being a spark you have not listened to Steve at all 1 circuit only trips on E7 board regardless of what MCB is used in it 2 same circuit same heater same switch works fine on RCD protected board with same size MCB 3 fault must be on E7...