Please help. I have a basic understanding of electirics, but 5 Electricians are stumped and I don't know where to go next. My mother in law heats her house by 4 Night Storage Heaters, all of which are wired to a Economy 7 supply/fuse board, with no RCD just MCB. The largest of the Night Storage Heaters began to fail and trip the MCD. To cut a long story short, she ended up having a new one fitted. Unfortunately this new one also now trips the MCB. The electricians have tried swapping the various supplies to the various heaters around in the E7 fuse board and the same heater is tripping the different MCB. It would be an obvious thing to consider that there is a fault on the circuit between the board and the night storage heater. However, they have now wired it into the day time board and it is not tripping. Has anyone got any ideas as we need to get it wired back into the E7 circuit??
 
This will be my last post on this

First time we were called to fault with storage heater there was a live to earth fault on the existing cable fed from E7 consumer unit on a 16 amp 60898 MCB I’m not sure what the installation resistance was I didn’t go

Deakon ran a new 2.5 cable to heater that then worked for 4 day before tripping the 16 amp 60898 MCB.

Then we had the callback the next day and the day after we then installed a new 2.55kw heater
And put it on same MCB

Still tripped I went back as you know was getting voltage drop top of main switch constant 230v bottom ov main switch fluchuating between 210v and 235v ( there was a very low bussing Sond coming from main switch ) clamp meter going up and down 13amp to 16amps

Voltage did not fluctuate until 4th new storage heater was energised the new one (dint know why this is a mistery to me as much as you)

MCB did not trip when I was there for 30 min before E7 when’s of at 7pm when main switch changed

Worked last night we rang customer this morning and storage heater nice and warm

It’s not something I would believe myself but I was there and that’s what was happening

I hate ELECTRICS LOL

Merry Xmas every one
 
This will be my last post on this


Voltage did not fluctuate until 4th new storage heater was energised the new one (dint know why this is a mistery to me as much as you)

MCB did not trip when I was there for 30 min before E7 when’s of at 7pm when main switch changed

Worked last night we rang customer this morning and storage heater nice and warm

It’s not something I would believe myself but I was there and that’s what was happening

I hate ELECTRICS LOL

Merry Xmas every one
Well, fault proven or not, if everything works and tests OK, they should have a warm and safe Christmas.
Same to you. Enjoy!
 
5pm !!
that's the time the annual christmas arm wrestling competition starts.
Have a good one !
Well, fault proven or not, if everything works and tests OK, they should have a warm and safe Christmas.
Same to you. Enjoy!

just finished a callout to one of the less affluent areas of the city, their neighbour had their door kicked in and all the presents nicked, could be worse!
 
a) Dissapointed..No answerer to Marconi Post 187 Item-(d)
b) (reminded of previous Xmas break-ins "Tower block hell"- .......Cheers " El -sp " -I'm NOT travelling this year)
c) still sensing a non-resistive aspect (-Half facts-/vagueness)
-- Have Booze so will enjoy Xmas--
( Now suffering last Post disease--echolalai-varaint-B)
 

Reply to Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
264
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
753
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
239

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top