Search results

Search results

  1. E

    RCD / LED problem

    That's right. LEDs are on the walls and don't suppose to have anything to do with the Beds.
  2. E

    RCD / LED problem

    It's costing me a lot cause the place is 100 miles away. Only agreed to do it because the owner is a friend of a friend. Big mistake.
  3. E

    RCD / LED problem

    You are absolutely right about not giving a customer an option in this case. I will be there next week and try to get an earth leakage metre too. They are not cheap but seem very useful.
  4. E

    RCD / LED problem

    I did want to fit separate RCDs for each bed and explained to the customer why. He wasn't happy with an extra cost.
  5. E

    RCD / LED problem

    Sorry. Sent it twice.
  6. E

    RCD / LED problem

    That is the whole point of this thread. The LEDs don't suppose to have anything to do with the sunbeds but they DO. EVERY time the LEDs are off, the beds trip an incomer RCD. EVERY time the LEDs are on, the beds work fine. LEDs are in the separate consumer unit and are not connected to the...
  7. E

    RCD / LED problem

    The sunbeds are connected to 5-pin interlocked sockets. RCD is required by the customer and the installers. Yes. I am an electrician.
  8. E

    RCD / LED problem

    It could be a bad idea but I have seen five beds running on a single RCD without any problems. But why a light circuit in a separate consumer unit affects an RCD which it isn't wired to (without tripping "its own" RCD inside CU)?
  9. E

    RCD / LED problem

    And thanks for such a quick reply. I wasn't expecting it.
  10. E

    RCD / LED problem

    Don't have earth leakage clamp metre but might get one. RCD required by the customer, apparently something to do with insurance or council. RCD incomer feeds only the four sun beds. There are no other circuits in DB.
  11. E

    RCD / LED problem

    Hi, I'm new to this forum and I would like to get some advice. I was asked to install a 6 way DB feeding four 3ph tanning beds. I installed the board (Hager 100A 30mA RCD as incomer, C32 MCBs )and isolators, tested the system and left. The sun beds installers team arrived this morning. After...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top