Hi,

I'm new to this forum and I would like to get some advice.

I was asked to install a 6 way DB feeding four 3ph tanning beds. I installed the board (Hager 100A 30mA RCD as incomer, C32 MCBs )and isolators, tested the system and left. The sun beds installers team arrived this morning. After connecting the beds they rang me and said that three of the beds trip an RCD when on standby. They also said that they are sure the beds are fine. Every time they tried to start any of those three beds an RCD tripped.

The rest of the electrics in the unit are fed from a single phase (L1) CU which was already there. One of the circuit in this CU is B6 MCB feeding about ten cheap ebay LED drivers for LED light strips. There is no switch on the circuit so those LEDs are being switched on and off by operating an MCB.

The bed installers noticed that with this LED lights circuit being OFF, the RCD incomer on DB trips when they turn the beds on. With the same light circuit ON, the beds seem to work fine.

DB and CU are two separate units. Have any of you ever came across anything like this? I'm going there early next week to give it a good check and I'm trying to build some plan of action.

Any ideas?
 
CU is B6 MCB feeding about ten cheap ebay LED drivers for LED light strips. There is no switch on the circuit so those LEDs are being switched on and off by operating an MCB.
b6 not c6 then or 10amps?
The bed installers noticed that with this LED lights circuit being OFF, the RCD incomer on DB trips when they turn the beds on. With the same light circuit ON, the beds seem to work fine
wired up wrong !
 
Don't have earth leakage clamp metre but might get one.

RCD required by the customer, apparently something to do with insurance or council.

RCD incomer feeds only the four sun beds. There are no other circuits in DB.
 
Don't have earth leakage clamp metre but might get one.

RCD required by the customer, apparently something to do with insurance or council.

RCD incomer feeds only the four sun beds. There are no other circuits in DB.
What are the sunbeds connected too? (eg socket)
Why have the council stipulated RCD protection?
Are you a electrician?
 
It could be a bad idea but I have seen five beds running on a single RCD without any problems.

But why a light circuit in a separate consumer unit affects an RCD which it isn't wired to (without tripping "its own" RCD inside CU)?
 
The sunbeds are connected to 5-pin interlocked sockets.

RCD is required by the customer and the installers.

Yes. I am an electrician.
 
Hang on is the RCD required by
1) insurance
2) council
3) customer
4) installer

You have told us 4 different things in the space of 5 minutes
 

Reply to RCD / LED problem in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
685
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
682
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top