Hmm can't see the (iv) point, explain how? Identification or ability to hold the gas pipe at a safe potential? I think the term 'considered' means in this context considering its suitability after the original installation, rather than being originally considered (and hence designed) for the...
Only joking about the tied on earth! Temp installation certainly does have to be just as safe as permanent, question is more what constitutes compliance with clause (iii) - 'Unless compensatory measures are provided, precautions shall be taken against its removal' - that's in relation to using a...
Boiler and gas is currently all outside so no requirement for bonding - that said it's all bonded anyway, CHS pipes need bonding so are so where they run past MET, where they get to the outside boiler the gas is bonded to them just for good measure. Now boiler is coming inside so gas will too...
Interested in opinions on this. Need to put the boiler (in my own house) in a temporary location for 6 months while an extension is built, when it will go in the extension. Running a dedicated 10mm to the temporary location will be a pita, and entirely unnecessary since I already have what...