Search results

Search results

  1. mrloy99

    Query; I have a panel board(mccbs) containing 100amp mccbs...

    I'm just the tester on the job. I still have't seen the switch rooms. I'm guessing that these are existing breakers at their lowest settings.. I'm just used to seeing a breaker at the origin that would protect the cable. I'm asking will they disconnect under fault conditions. I'm not sure the...
  2. mrloy99

    Query; I have a panel board(mccbs) containing 100amp mccbs...

    Hello engineers. I have a query. I have a panel board(mccbs) containing 100amp mccbs supplying various "life safety DBs" lifts, water mist pumps etc.The panel board has an MCCB of 250 AMP as the main switch. It is supplied from an ATS in 120mm sq.4 core with 70mm earth.A run of 20m.The ATS is...
  3. IMG20191006145507.jpg

    IMG20191006145507.jpg

  4. mrloy99

    Unable to separate wires on ring circuit

    Agree with Conlok coupler and bush. You have no mission threading it. Conlok will slide on. Only one half of it is threaded
  5. mrloy99

    Zs reading does not meet current regs

    The increase in loop impedance from. 0.20 at the DB to 0.79 on a 10m run sounds like something not right ,loose connection ?As another poster suggested. Try testing with probes at the socket terminals. But having the RCD ..it will be fine. ..⌛
  6. mrloy99

    Help!!! Can't turn electric off!!!

    No update yet then?. If it's a flat that was devided up from the main house at one stage.Maybe you are on someone else's supply.. Yippee free lecky.Is everything else in the house off when the main switch goes off?
  7. mrloy99

    Dangerous upgrade to crabtree rcbo's

    Only if the neutral is disconnected at mains
  8. mrloy99

    Contactor control circuit

    No doubt I'm missing something here but the ones I've done, are switched from the surgeons panel and just come on at the same time as the socket, not on the control circuit. I don't think there is a requirement to provide a fail safe mechanism. A buzzer might be a better warning than a lamp.
  9. mrloy99

    Irish job query for testing

    Oh dear...Thanks...looks like we will need to get an inspector to inspect the inspector
  10. mrloy99

    Irish job query for testing

    Thanks Andy,but I think you are missing the point...I am not using BS6761 sheets
  11. mrloy99

    Irish job query for testing

    Hi I have a testing job to do in ireland.The test sheets i've to use ask for the R2 reading only..not R1+R2.....It is impractical to use the long wander lead method so I was thinking to work it out from R1+R2-(R1+Rn)/2=R2.........I was thinking to use this as opposed to R1+R2/2 to take account...
  12. mrloy99

    Is a borrowed earth allowed?

    There are other concerns too..maybe there could be another radial in the kitchen with a 'lost ' earth and the previous spark has already borrowed the cooker earth......So new cooker circuit in /old cooker circuit out might leave another circuit unprotected...Full test might identify that..I...
  13. mrloy99

    SWA in drain permissable?

    Agree..solar is the way forward for this instal.just screw it on the wall.job done..no pole required.Don't even need a test cert.
  14. mrloy99

    Anyone go the BBB to hand - reg regarding mix and match

    Are they nessary under the regs..I dont think so unless the cable is buried. Or is munufactors instruction Although I always do fit myself.
  15. mrloy99

    Hi from a gran with a dodgy socket.

    Presuming that the plug is now removed...it is up to the landlord to ensure the installation is safe for the next tennant as he is required to have the place inspected/tested
  16. mrloy99

    Test failed due to missing RCD

    Hi Peter I haven't read all of the posts on here so please excuse if this has been covered already. I'm fairly sure it is indeed a legal requirement on change of user to have inspection carried out. The code should be C3 for no rcd for socket outlets.C3 for no rcd on bathroom circuits and C3 for...
  17. mrloy99

    Test failed due to missing RCD

    And leave the rest NOT covered? Surely bathroom lights have been reqd to have rcds for at least 10 years and the rest needs it for cables buried in walls
  18. mrloy99

    Test failed due to missing RCD

    And leave the rest NOT covered? Surely bathroom lights have been reqd to have rcds for at least 10 years and the rest needs it for cables buried in walls
  19. mrloy99

    Wiring for 14kw range oven

    14kw sounds really big cooker for a private house...housing association?Is it an HMO? If so it may not necessarily be considered as domestic as there could be more than one person cooking at once so your normal allowable diversity of first 10 amps plus 30% of the remainder wouldn't be...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top