Hi Steve, thanx for post,
was more concerned about safe isolation at house end, forgot to mention load on lighting.
No more than 1Kw tops absolute max!! Couple/ three 100watt halogens, couple of elv circuits, and room for expansion, so 1000/230= 4.35amps max
18mv/am x 4.35a x 35metres = 2.7%...