Can someone tell my the test sequence should be done on a periodic inspection on a domestic house i have a megger 1552 and new to test and inspection meny thanks.


When entering into an agreement for the Periodic Inspection and Testing of a building under your control it is a fundamental requirement that the extent and limitations of the inspection and testing be fully described for the client. It is recommended that the following procedures are adopted and that the relevant points be discussed with the client prior to completing the inspection.
Determine your requirements for inspection and testing and tailor the procedures accordingly.
As it is neither practical nor possible to inspect all parts of the installation, a sampling process should be employed, normally in the order of 10% of all accessories, lighting fittings and control equipment.

Detail any limitations of the inspection and testing to be carried out and explain that the installation must not be dismantled in any way other than opening equipment covers, and that the building structure must not be disturbed. This means that concealed cables and equipment will not be inspected.

Visual Inspection

Check for any obvious mechanical damage or deterioration of materials and equipment, exposed cables and live parts, missing covers, fixings, labels and notices etc.
The main switchgear and all distribution boards. These should be inspected for the following:
Fuses and MCBs are correctly rated for over-current and fault current
Fuse and switch contacts are clean and have not been over-heating
Conductor terminations are tight and correctly lugged (if possible)
Busbar connections are properly made and clamps are tight.

Cables - whenever possible cables should be inspected to ascertain:
The suitability for the load and operating environment The condition of the insulation and protection Adequacy of fixings and mechanical protection Suitability of glands and shrouds Proper use of earthing clamps and earth connections. Any signs of over-heating and damage.
Equipment, accessories and lighting fittings should be inspected for:
Deterioration due to the atmosphere, mechanical damage, over-heating and adequate fixings. Connections of conductors and condition of flexes. This should include removing light fitting covers, switch plates, socket outlets and covers of equipment.A sample of approximately 10% of all parts and areas of the installation should be inspected.
Testing

Continuity of circuit protective conductors (CPCs) at all metal accessories and equipment within a height of 3.5 metres from floor level, and at 10% of all lighting fittings.

Continuity of all bonding conductors and earth clamps.

Continuity of all ring circuit conductors, including CPCs.

R1 + R2 continuity test or R2 test on every final circuit.

Insulation resistance between live conductors and earth of all circuits collectively, excepting any circuits supplying electronic equipment which may be damaged by the test. These shall be listed separately as not having been tested.

An electrical separation test on all electrically separated circuits.

Polarity at the board and at a 10% sample of all lighting switches and equipment to ensure that switches interrupt only phase conductors.

Earth fault loop impedance (Ze) at the main intake position.

Earth fault loop impedance (Zs) at each distribution board.

Earth fault loop impedance (Zs) test on every final circuit and every socket outlet.

Test all Residual Current Devices.

The resistance of every earth electrode.

Prospective fault current at the main intake position and at every distribution board.

A manual operation test on all MCBs, RCDs, switch fuses andisolators.
 
Last edited:
the tests for a pir in any order take a look at GN3 starting at page 73 table 3.3

It certainly says that in GN3 but I think its a little misleading.

As the installation is already live then carrying out live tests before dead is no problem.
But when it comes to dead tests IR should always be after continuity tests, never before.

If there was a break in the CPC an insulation test will only test up to the break and test results will appear good.
So its important to do continuity tests first to ensure that when IR tests are done, that the entire length of the cable is being tested.
 
Periodics

Ze and PFC on entry with visual on supply. Note this on the form

Next fuseboard and circuit descriptions

Dead test, record

Live test, record

put everything back, pack your kit and be on your way ;)
 
Last edited by a moderator:
easy way to remember test sequence is CRIPPLER

Continuity
Ring
Insulation resistance
Polarity dead
Polarity live
Loop impedance
Earth Electrode
R.C.D.
 
The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

Darking,
isnt that sequence for new installs?
I thought it was different for P.I.R.
someone will carify and shoot me down in flames!!,
cheers
mick

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.

The difference between a PIR (Report) and an EIC (Certificate) are your cover sheets. The Schedule of Inspections and Schedule of Testings are identical in both cases.

As you know, the PIR is issued for an existing installation, often with no records or Schedules available, so a comprehensive knowledge of the type of installation is necessary to make a competent assessment of its condition, followed by an initial sampling of tests to confirm the visual assessment, and if these are not satisfactory more intensive tests should follow.

For an EIC the installation should be inspected and possibly some testing at various stages ie first fix, second fix and when commissioning the new installation. I hope this is helpful.
 
Last edited by a moderator:

Reply to test and inspection sequence in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

Thanks Risteard. I had put it down as a 2, even though I wasn't sure if I was right in doing so. Good to hear you'd have done the same. Thanks for...
Replies
8
Views
1K
  • Question
Thanks mate this helps a lot, especially with the 2 board but real life scenario they being in separate rooms
Replies
4
Views
359

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top