They are 3 phase 36kw / 53A per phase, there is 8kw 3p dishwasher, 15 ceiling panel lights and sockets for display chiller units and fridge and freezers
His going for just 2 at moment, very little else in there gas for water, small vent. So cookers will be 93A for 2 (100% + 80%) . Not worked in many restaurants what's everyone opinions. His hoping to upgrade later on to 200A
Nothing else big in there at moment just display chiller units, no vents and small water heater for sinks. The ovens I worked out using 100% for 1st then 80 and 60 which is over the 100a supply without anything else
They are pizza ovens, that's what I work out 53a each phase there is not much else in there I thought it would be pushing it have all 3, in case all come on together
Hi, been asked to install 3x 36 kW 53A ovens and 9 kW 3 phase dishwasher in a cafe 100a 3 phase supply. I think the best way is to have 2 ovens on a change over switch so only 2 can run at once, but he wants all 3 but I think it will be to expensive to upgrade. What does everyone think
Thanks...