Hi, been asked to install 3x 36 kW 53A ovens and 9 kW 3 phase dishwasher in a cafe 100a 3 phase supply. I think the best way is to have 2 ovens on a change over switch so only 2 can run at once, but he wants all 3 but I think it will be to expensive to upgrade. What does everyone think
Thanks for help
 
allowing for diversity,ovens will be switching on and off due to thermostats. should be OK. try switching each one on in turn and clamping the supply tails.
 
Hi, been asked to install 3x 36 kW 53A ovens and 9 kW 3 phase dishwasher in a cafe 100a 3 phase supply. I think the best way is to have 2 ovens on a change over switch so only 2 can run at once, but he wants all 3 but I think it will be to expensive to upgrade. What does everyone think
Thanks for help
36kW is a hell of a big oven. Are these cookers, with rings on top?
 
36kW over 3 phases is 53A/phase approx, so a 100A/phase supply will be adequate, depending on what other loads will be in use.
 
They are pizza ovens, that's what I work out 53a each phase there is not much else in there I thought it would be pushing it have all 3, in case all come on together
 
Hi dude,seems strange that an operation with three of those ogres,would not have requirements for heating,lighting,washing,ventilation,warming and a phone charger ;)
 
They are pizza ovens, that's what I work out 53a each phase there is not much else in there I thought it would be pushing it have all 3, in case all come on together

You think it would be pushing it?
How about some calculated values rather than an 'I think it would be' kind of guesstimate?

What diversity factor have you established for this?
 
Nothing else big in there at moment just display chiller units, no vents and small water heater for sinks. The ovens I worked out using 100% for 1st then 80 and 60 which is over the 100a supply without anything else
 

Reply to 3 36kw cookers in cafe in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
I have sent you my contact details where in the West Midlands are you? I am based north of coventry but travel the county and beyond you may...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top