This touches on the debate about exactly which figure the Feed In Tariff calculations are based upon (sorry!):
If we install a "Power One Aurora PVI 3.6 Outdoors 16A limited" inverter with 18 No. 250W (4.5kWp) Yingli Solar panels the Aurora configuration tool tells us the inverter is optimally...
Hi guys,
Some of PV installators told me that they want 4KW inverters with the max out put of less than 16A/phase. But G83 defines that is the reuqirement to systems less than 3.7kw. For 4kw, the safty should be G59. Could anyone tell me why some installators hope to get 4KW under 16A...
Hi guys,
Some of PV installators told me that they want 4KW inverters with the max out put of less than 16A/phase. But G83 defines that is the reuqirement to systems less than 3.7kw. For 4kw, the safty should be G59. Could anyone tell me why some installators hope to get 4KW under 16A?
Thanks...
I was always taught that the max size mcb for domestic type lighting circuits is 10A due to the fact that accessories are rated no higher than 10A. When I recorded 16A MCBs on lighting circuits as a C2 departure my supervisor has corrected them as satisfactory as the current carrying capacity of...
10 x wall mountable female outlets.
eBay - The UK's Online Marketplace
3m extensions
eBay - The UK's Online Marketplace
Extension/doublers
eBay - The UK's Online Marketplace
Can do a deal with forum members, be a shame to bin it.
Sorry to put this up as I do not have enough information, just after some thoughts really.
Have a house where they want some additional sockets and looking at the CU (16th edition) there are two 16A circuits with two cables (2.5mm2) coming out from each, OK I thought two 16A RFCs, bit odd.
In...
Due to supply problems I ended up panic buying a Chint CPS SC4KTL-O. I took it out of the box today and noticed a G59 sticker. I called Chint, too busy to talk to me (also were very rude, and knew next to nothing). Someone useful was going to call me this afternoon but nearly 11pm so I'm...
I have a quote which I would like to go ahead with, but with the proposed cut off with fits, will the below system have any problems with SSE DNO and how would I complete the application form to ensure no problems as there is no space to state two invertors. or would it be safer to reduce by...
Howdy
I've come accross a situation where 16A MCB have been specified for ring circuits. The rings serve socket outlets having looked through the regulations I have been unable to locate any specific requirement stating that they can not be used, however, I would be grateful for some...
I have 7xM.K 230v Blue 16A RCD commando sockets, all installed for less than 24hours!!!
All installed as part of a factory fit, only to get the phone call the next day to point out that all the plugs were req to be 32a not 16a!!!
Of course the wholesaler wont have them back so if any wants any...
The saga continues. I was told today by an engineer at Central Networks that it is inverter output that is important when considering the G83 threshold.
Hopefully this will be the stance all DNOs take before long.
Can anyone tell me why the latest 17th edition 10 way consumer units have all but 20A MCB's? They seem to have a couple of 16A MCB's but for a radial 20A is more desirable.
Im confused. Its a great package but whats the 16A breakers for? And why no 20A breakers?
Right theres a good chance I could be picking this up wrong, but I'm sure this was what was said. Boy in my college class said he spurred off a water heater circuit (3kw) for a socket for a 2kw fire. Surely this can't be right?
Can anyone help? got old MEM Memera 21 board , a 16a mcb broken (type 1) . Wholesalers can't supply under £40.00 as now (type 3). Halfway through Level 3 CG2330 (Confident to change/upgrade board). At this stage would rather replace Mcb? ,any advice very grateful.
Hi Guys,
Firslty i'm new to the forums so hello and hope you're all doing well.
A quick question on the size of the HO7 flex I need to use for a splitter that will have a 32A Comando Plug on one end and two 16A Sockets on the other.
Would I be right in saying that each split will need 2.5mm...
Am i allowed to install a radial circuit that supplies 1 single and 1 double socket in a garage with 1.5mm cable?
It is unsheathed cable in plastic conduit (ref method B). From the BRB this has a Current Carrying Capacity of 17A. It is on a 16A MCB and the load it supplies will be a freezer...
This is my first post so Hi to all
I have to wire in a couple of 16 amp 3 phase wall sockets in a work shop.
The ones I have been given are 4 pin.
If I run Line 1, Line 2, and Line 3 standard brown Black Grey I am guessing the 4th pin is for earth and power is between each phase?
Just...
Does anyone have an ABB MCB 16a i could buy off them? I have been to my suppliers and they want £75 for one as ABB have a minium order of £50 plus p&p or does anyone know if any other makes fit?
Just a quick one, all my books are in college.
Is it acceptable and up to current 17th to use 16A on a radial. Wired in 2.5 T&E, short run (8M) with 3 sockets.
I have used 20A in all other flats (6 of), but got to the last 2 flats and ran out of 20's, so my colleague put 16's in. I'm 99.9%...