Industrial installation (non-domestic). Here's the scenario:
A large (150kW) 3-phase motor circuit where the supply is taken from a starter fitted with 315A BS88 HRC fuses.
From calculation using the cable data, the Zs value exceeds the manufacturers requirement for 5s disconnection time...
Steveb555
Thread
3-phase
bs88
circuit
fuse
fuses
high zs
motor
question
regarding
using
I want to try and replace the standard relays on our holding pots that are being kept hot by elements. I want to use thyristors instead, but i'm not sure what the best way would be. I would like to implement zero crossing control. So when 1 is fired in the forward dirction, 2 and 3 should be 1/3...
Couple of weeks ago I signed a lease on an industrial unit (all 25 units in the building are 'wired for 3-phase').
Although the unit had a single phase CU the wiring was there for 3Ph.
Spent the last week installing a 24way DB, sockets, isolators etc. etc. etc., got it all checked and...
Wardie
Thread
3-phase
building
canada
change
connection
meter
phase
units
Hi! I have recently changed my job and my employer has asked me to survey the existing electrical system. The main incomer is 100A 415V 3-phase and neutral and each phase and neutral is attached to a separate CU. This is how is breaks down:-
L1+N= (100A CU) Handdriers in toilets, lighting...
If you are running a single phase board in a commercial premesis, its the only board in the place, but the incomer is 3-phase with a 3-phase meter but only single phase leaving the meter, would you still double the KA?
I've got a boat, and often connect to shore-power using a 230V IEC blue 16A plug like this:
A lot of places now have IEC sockets that take a 415V 3P+E red plug like this:
Can you get a converter, I'm guessing it would be a transformer?
I have the following:
Extension Ring 32A
Up Ring 1 32A
Up Ring 2 32A
Down Ring 1 32A
Down Ring 2 32A
Kitchen 1 Ring 32A
Kitchen 2 Ring 32A
cooker 1 32A
Cooker 2 32A
Shower 16A
Up Lights 1 6A
Up Lights 2 6A
Up lights 3 6A
Down Lights 1 6A
Down Lights 2 6A
Down Lights 3 6A
Smoke...
For phase to phase Meggering of 3-phase Synchonous Generator, we have to open its flexible links (between phases) & its star point. We then connect Megger's positive lead to phase (which we want to Megger) & we short remaining two phases with ground?(& connect megger's negative lead to it) Why...
Hi guys, I've just been given a date for EDF to come and connect 3-phase supply to my garage at home (I'm starting my own business and unfortunately the control cabinet I'm designing needs 415v 3p, so to hold off renting a unit I thought I'd power-up and test the machine at home).
I've sourced...
Hi all,
Got an interesting generator related issue here………………. I’m currently helping a friend with a 100KVA geni and I’m after some advice. I’m trying to work out what the maximum current draw would be…………..
So if O\P Amps = KVA / (O\P Volt / 1000) = 100/(240/1000) = 416.66 Amps
But as...