3 phase

  1. J

    Measuring 3 phase usage with a clamp meter?

    Good morning, I have a 3 phase supply into my workshop Hager dist board. I need to measure my usage for business accounts. My Electrician mentioned clamping around the swa cable with a ct clamp would be a simple metering option, but I'm not sure if I understood him correctly. Is this...
  2. L

    discharge higher than 3kw with ac coupled 3 phase

    hi guys i'm trying to get my head round the following setup growatt TL3 5kW 3 phase string inverter 14 panels @ 395W Spa3000 TL ac coupled controller - unless there is a alternative mcs approved one available growatt ark 4x2.5's with bms will i be able to draw 3 5 or 8kw with this setup please...
  3. D

    3 phase run of 1300 feet

    Hello all. I am trying to get 125 amps 3 phase back to a paintball field to power an electric air compressor. I have a 3 phase 120/240v PG and E feed, 200A panel about 1300' feet away from the desired location. I have 2 transformers, so we can transform up to 480 to make the 1300' run, and...
  4. H

    3 phase motor cable size

    Hi all, I’ve been asked to run a cable for a 3 phase DC motor. Not having much experience with motors would you work out cable sizing the same? In the picture attached are the details I have received. Any help would be great 
  5. J

    3 phase load balancing

    Hi all, just looking for an outside opinion on this. A collegue and I are going to be installing 4 three phase EV chargers on a site. He's of the opinion that we will need to invert the phase at each charger in order to balance the load, i dont believe this is correct as equipment with 3 phase...
  6. K

    Direct Buried Cables 3 Phase

    Hi, I am a mechanical engineer tasked with some electrical engineering scope of work and not sure where to look for information on the following... I have 12 x Off 95mm2 SWA 3 Phase cables coming from Solar inverters into an energy building panel. Each cable is carrying a maximum of 160Amps...
  7. timhoward

    Compact 3 phase distribution?

    I may be seeking the holy grail here, but does anyone have any instant thoughts for a compact 3 phase distribution board that doesn't cost the earth? I only need 1 outgoing 3 phase distribution circuit and 1 single phase final circuit, with an 100ma RCD main switch. This is all outdoors with...
  8. E

    Purpose of 110V 3 phase?

    Hi, I have taken over a design engineering job for industry. The design is using a 400V/110V transformer. Usually, the 110V is single phase. However, in this case it is giving 110V 3 phase 32A. The 110v 3 phase is for use with 4P 110V socket to run a pump. Being in the UK, I am used to...
  9. Y

    3 phase generator help

    Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator has 3 motors 11hp, 5.5 hp and 3hp. The 11hp motor kept tripping the gennys mcb so a previous spark fitted an adaptable box with contactors so it now...
  10. F

    3 phase meter question

    Hoping to get some info on 3 phase meters. Family has a place out in the country. It needs to get the meter replaced, but seemingly it's a 3 phase meter. Scottish Power has organised this but have cancelled the job as none are available. So my question is, could the job not be done with an...
  11. Z

    Wiring diagram for 3 phase contactor start up

    Hi all, I have two three phase sanding machines that both have there own contactor start up. Both work fine. I have connected a dust extractor to them both. That also has its own contactor start up ad works fine. Its also 3 phase. How can I wire the the extractor to be triggered by either...
  12. B

    PAT Testing 3 phase to 13amp adapter leads

    Hi Hope anyone can help Can someone give me advice on how to connect up a 3 phase to 13amp adaptor lead for carrying out PAT testing on 3 phase equipment but using a 13amp port on the PAT tester. Need to know the connections for 4 pin 3phase & earth plug to 13amp plug 5 pin 3phase &...
  13. C

    UK I'll soon be installing a 45A 3 phase deep fat fryer at the school where I work.

    I'll soon be installing a 45A 3 phase deep fat fryer at the school where I work. The run is approximately 7m from the DB, and the cables will be enclosed in empty trunking. What size cables will I need?
  14. newfutile

    3 phase SPD MCB size

    Does anyone know what size cable to use for a MCG type 2 SPD (3 phase) and what MCB.the manufacturers instructions don’t state any values! also should i use 3 x single phase or a 3 phase MCB?
  15. D

    Where do you test from in phase rotation test on am2

    About to re sit testing section of am2. Am I required to test phase rotation at the incoming switch and also the 3 phase socket and motor. Just can't seem to find any clear instructions on what they expect on this test
  16. B

    Need to convert 3 phase 480 60 hertz to European 3 phase 330 50 Hertz

    Hi , I have a customer that has purchased a machine from Turkey. The machine requires 3 phase 330 volts at 50 hertz. I have access to 3 phase 460 at 60 hertz here at the plant in the US. I can find a transformer for the voltage but that doesn't change it from 60 hz to 50 hz. Im looking at 90...
  17. J

    3 phase rotary inverter from single phase.

    My 3 phase cnc lathe is rated at 27 Amps on the manufacturers website. When I mentioned that I want to run from a single phase via a rotary inverter I was told that it will need 27 A per phase therefore 3x27=81 Amps from my single phase. Is this correct? I reckon the machine is about 5hp.
  18. M

    Costing running 3 phase motors

    Been asked to cost the running a number of motors . Was going two amp test each phase and multiple by line neutral voltage to get kWh . Is this correct .ta
  19. R

    3 phase sub main…help please??

    Hi All I’m in a bit of a quandary at work and need a couple of things clearing up if poss. I’m the maintenance manager/spark/fitter/skivvy/everything else that needs doing man 🙄 in a plastics factory and I’ve got to provide a supply for a new machine. The current set up is a 90mm SWA protected...
  20. W

    Proteus 3 phase DB horizontal

    Have any of yous fitted the proteus 4 way 3 phase DB? The horizontal one. The din rail I got with it was very narrow, only the top off of the RCBO clipped onto it. Anyone else had this?
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top