Hello, This is the first time iv came across anything like this and i went to quote this fuseboard for a upgrade yesterday and had a look inside and did all the required testing and inspecting and said id get back to them with a date when i can do the installation but came across one slight...
elecypwn
Thread
andearth
aus
conductors
cpc
earth
old
twin
twin andearth
Greetings,
Is this allowed?
It would appear from BS7671(17th) that the installation reference number is 8 or 9 with a reference method 'B' for determining the current carrying capacity of the cable. However, the anomaly is that table 4D5 doesn't include a column for method 'B'.
Can anyone...
hi Guys
any ideas what code you would issue (if any) for 3 phase neutral and earth circuit ran through two TW+E cables, the circuit is supplied via a 3 phase mcb (the blue of one cable is used as the L2, its ran through trunking throught its route,
i know its not good practice but is there...
R4BOE
Thread
3 phase
andearth
cable
circuit
code
earth
neutral
phase
through
My parents appear to have a twin and earth cable connecting the main switch to the CCU, it has two earths both of stranded copper, but twisted together separately. I think the Lines are 10mm2.
Anyone seen this before?
I have a reading of 5ohms when checking resistance between neutral and earth, it's a TNCS installation. Is this a little low? I checked this after finding spurious readings on a central heating boiler, whilst doing preliminary electrical checks. Any help, anyone
NEUTRAL EARTH FAULT
I would just like to correct my message title for me mucking up :13:
A guy I work with was sent to change a mains board the other week. He isolated the supply and proved it was dead, He started stripping the board out and got a zap! He checking and noticed he got 230v...
millar
Thread
230v
andearth
aus
between
cable
earth
incoming
insulation
live
supply
socket ring wired in 3 core and earth - seems to be 2.5mm in old colors - the third core is blocked at each end. do sockets have to be in 2 core and earth or not? As the ring is being extended is this all going to be have to taken out.
Hello everyone,
Have been inspecting caravans statics at a 200+site. The levels of ZE are 8+ ohms at the caravan hook up and it is on a TT system (the incomming mains) to 4 or 5 submain distribution points where there is a common earth rod and from there via swa using the cable core or armourmed...
mcmainelectric
Thread
andearth
aus
caravan
earth
electricians vans
rods
system
tt system
van
vehicle
I am working in a small industrial unit which is being converted into a kids go kart track the lighting is currently wired in twin and earth pvc cables clipped along the steel beams. The place needs to be tested and certificated is there any issues with wiring in twin and earth along steel beams...
I don't normally install twin and earth so need some advice. If a 10mm twin and earth is correctly sized and installed to the correct methods should it get warm. Thanks
I am just completing my first install for my forthcoming MCS assessment. It is a 690w system.
1. Am I ok to run the cable on the AC side of the inverter in 2.5mm cable (as it is only 690w system)?
2. I need to earth the array as it can be touched from a velux window. What cable size for...
TN-S system. 20m run of 4.0mm SWA to ne CU in garage, supplying 3 lights and 4 sockets. RCD protected, lights on 6A breaker, sockets on 20A breaker.
Does this need and earth rod and why?
Why is the 3rd core of SWA not effiecient?
I'm confused because reading some older posts people are...
Electricalserv
Thread
andearth
aus
bonding
confused
earth
fuse
garage
garages
rods
supply
Have been installing new 20 amp radials for socket outlets and lighting in a newly built office space in a small commercial unit. The new build office is part of a much larger building, and although it has its own CU, this in turn is fed from a 3 phase DB situated in the warehouse area, which in...
Evening,
I have a class 2 light for the bathroom, and it has its own L & N wires that go into connectors in a type of small chocbox, that go into the loft. Whats the best way/regulation to terminate the incoming earth?
Cheers
CRAIGNEWHAM
Thread
andearth
aus
class
class 2
earthearth wire
light
wire
I posted the other day regarding advice on a switceh fuse for when the CU is a distance from the meter.
I've decided on using a 60amp switch fuse which will be fed with 25mm tails. From the switched fuse to the CU, roughly 9-10 meters, I have specced 10mm 2 core SWA and a 16mm earth. The supply...
Hi,
Is any body aware when LSOH SWA cable to BS6724 first introduced to the UK? Also, is anybody aware of the copper sizes that were available for the bare copper conductors used to bond installations in the circa 1960's? I am coding a PIR report and for my own knowledge I would like to know...
Hi all,
I have just been to price a CU change. The problem is the CU is about 20m from the mains position and is run in 16mm T&E. Here's the good bit the 16mm runs through a neighbours flat, so it can not be replaced and I can not run an earth next to it. I can, though not easily, run another...
Did a 1st fix to a rather large new build a couple of weeks back. It was a brick and block house which was going to be dotted and dabbed (If you know what I mean) on all of the external and downstairs walls. All good!!! So I decieded to run the tails (25mm) and main earth (16mm) on the block...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc