Hi Guys, needs some advice on a problem ive come across.
I am doing testing on a busy pub at the moment, I tested the flat DB yesterday and one of the ring circuits gave me these readings:
r1 = 99.9
rn = 0.51
r2 = 0.81
R1+R2 = 0.85
IR = >299
Zs = 1.10
As soon as I noticed the r1 reading being...
Dean31
Thread
advise
circuit
electricians' talk
fault
problem
ring
hi i was doing a job today and noticed that a plumber had done some work and he had spured off from the supply cable to the shower from the switch. In my apprentice days i was told that this should not be done and if i remember correctly it says in the regs
any advise to what to tell the client...
Hi All
I am in the processing of testing a house ready for a new C.U , all circuits check out ok but there is a plastic coated micc feeding a shed in the garden which is glanded onto the top of the original metal rewirable fuse board. I have to extend all original cables to reach the new cu (...
Hi all
My mate is having his council house reworked to current regs.
The bathroom has seven GU10 diwnlighters fitted, they are chrome with no earthing at all !!
With two of them in zone 1 above bath.
The council sparkles have stated they will fit new ones if he supplies.
What...
Afternoon all,
What are the differences in C and D types breakers (MCB's)?
What type would you say should be fitted to a refrigeration unit with compressor, lights, fans and a 800w drip tray heater?
We have some conflicting views in the office with some saying C type breakers should be fitted...