I need to calculate the true power and reactive power and i no the formula for true power is V x I x cos and reactive power is apparent power-true power squared. however the figures it have been given are the load size of 50KVA at a power factor of 0.7??? any help on this would be appreciated...
In a gas power plant There are 2 main transformers ( st1 , st2 ) taking from the grid 380 kv and step down to 13.8 kv ,and then feeding the main bus which it is divided into 2 buses ( A Feed by st1 , B Feed by st2 ) between them bus tie
st1 = 380 kv/13.8 kv
st2= st1
Bus A feeding gas...
in a gas power plant There are 2 main transformers ( st1 , st2 ) taking from the grid 380 kv and step down to 13.8 kv ,and then feeding the main bus which it is divided into 2 buses ( A Feed by st1 , B Feed by st2 ) between them bus tie
st1 = 380 kv/13.8 kv
st2= st1
Bus A feeding gas...
Hi all,
Where do I get phase (Z1) and earth (Z2) conductor impedances to calculate earth fault loop impedance?
I have seen (R1 + R2) tables which give combinations for cable sizes up to 35 mm2. What about cables > 35 mm2?
Can I use voltage drop tables (for phase conductors) from Appendix 4 in...
A student of mine had his new toy delivered today (delivery first thing, thank you very much Tester Meter). We've had a play with it and I am surprised to see that it has a method of caculating R1&R2 as what appears to be normal practice.
You turn the dial to Zref, make a loop impedance...
Just answered a question on another post ,and it dawned on me , yippee the brain kicked into gear , i have read on loads of posts that people say doing an inspection just calculate the R1R2 by doing a Zs and taking away the Ze , i have never liked this method and heres a reason why ...
Hi Guys
When checking a lighting circuit you obviously need to check at each point on the circuit, switch and light fitting.
What do you do when you can't get to the cable in the light fitting??
For example, in my kitchen I have 3 spot lights on a bar. I'm not able to remove the bar...
Does anyone know how to calculate the required distance between rows of modules to avoid any shading issues? I may need to mount the panels at less than 30° to avoid the need for planning permission and would rather not use mounts such as the Solion model as these waste valuable roof space...
My brains switched off chaps and i can remember how to calculate 3 phase kva
i know its V x I x 1.73 / 1000
so is it 230 or 400 x I x 1.73 / 1000
fee a right numpty cant belive ive forgotten it not done 3 phase calcs for a while please enlighten me to the correct figures then ill give my...
i need a optimal model for calculating arc fault current in low voltage switchboard.
where can i get a sample case of arc fault current ,so that i can calculate by different model of formula?
Hope that u all can help me....please!!!!
I guess if I knew the resistance of the Primary coil I could calculate it ? but wondered if anyone had a reference guide to current consumption when a 110V tool is not in use ?
ATB Steve
Hi all
My question is this
If a submain is run off the No.1 C/U to a No. 2 C/U, when we calculate the cable sizes for the C/U2 final circuits do we use the volt drop value of the sub main or do we use the 230v value ???
thanks for any help
john
Just wondering if everyone actually does a Zs test when filling in a schedule of results. In the OSG it says that you can measure it or calculate it by addition. I appreciate the different value stuff, just thinking it is a lot easier and quicker to be adding 2 figures together than taking...
Hi- I am looking for some help/ advice please. I'm confused about how How to calculate sizing of vacuum circuit breaker.
This project I work on it use 40m0A TP Vacuum circuit breaker to support pump 800 kW 11kV
I calculate the current just 49.4 A (800*1000/1.732/11000/0.85 ) I don't know...
Ok, many people come here and ask what they should be charging and how to work it out. I've been looking through my library and here is an excerpt from a book I found called 'The right way to start your own business'.
I have added some extra bits in there. I hope it's helpful to all those that...
Hi,
I know how to calculate volt drops on radial ccts, As a ring main is a loop and you ignore any spurs is there a voltage drop or is it considered to perfect or near perfect mains voltage regulation!.
How do you,or dont you verfiy votage regulation on a ring main when certifing that you...
I dont want go on about it too much as to what the positives and negatives are of calculating (or taking actual readings) when completing either a EIC, PIR or MWC...
Those of us who are testing on a very regualar basis will know the differences..
Im interested to know what method YOU choose...
Hi Guys
How do you calculate Prospective Fault Current??
Wouldi be correct in thinking it is nominal voltage divided by Zs + R1 + R2 ???
So
Nominal Voltage
Zs + R1 + R2
A
HI all.
I just sat the 2391 exam last night and was asked to calculate max zs for a 300ma rcd on a 230v commercial instalation im i right in thinking using ohms law 230v devided by 300ma devided by 1000 your thoughts on this would be gratefully appreciated...